  1. #14
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    4,764
    Yes, sounds low on charge. If you're experiencing cool nights and warm days, it will cool intermittently. Also, sometimes if you pump it down, you've backed up the refrigerant and it may work normally for awhile until the ambient drops. If it were me, I'd add a little gas. Your sight glass will clear once the headmaster kicks in. Make sure it operates correctly. Find and repair the leak. Charge the unit properly. There is a Sporlan document floating around this site on proper headmaster charging.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them

  2. #15
    Join Date
    Jun 2013
    Location
    So. Cal
    Posts
    58
    Thanks. Drop a little over 1 lb in and it kicked right in and cooled.