Results 1 to 13 of 22
    Jul 2013
    Benefits/drawbacks of oversizing heatpump Trane XL18I
    Most HVAC companies recommend a 3 ton heat pump for my house. If I went to a 4 ton unit - does the winter temperature of the balance point lower (any idea on by how much it will lower, 2000sqft house in PA)? I know my AC will short cycle - I do not care about this, I'm looking for the most efficiency in the winter months as heat is on for more months than AC. The unit will be a dual stage Trane XL18I. Are there any other drawbacks of over-sizing a heat pump? Thanks.
    Dec 2010
    Quote Originally Posted by racinkart2 View Post
    You'll get more heat from the larger HP. The balance point will be the same (I'm guessing) but you'll be using less back-up heat. The 2 stage operation will help during the A/C season. I'm assuming you'll be changing the furnace or the air handler (with a variable-speed blower) as well?
    Jul 2013
    Yes. I will be replacing the whole AC unit with a matching Trane heatpump & variable speed air handler as well. The existing heat is electric baseboards, I'd just like to use the heat pump as much as possible in the winter. Thanks for posting.
    Quote Originally Posted by George2 View Post
    The balance point will be lower.
    Don't forget. That there is a good chance that most of your duct work will need changed out. Along with additional supplies and return/returns added to move the additional air the 4 ton will need over a 3 ton.
    Madison, WI/Cape Coral, FL
    The low speed heat/cool air flow may be about right for your old ducts. High flow may be noisy. Like all a/c, you will need supplemental dehumidification to provide <50%RH throughout your home during low/no cooling loads and +60^F outdoor dew points. Prepare for 2-3 lbs. of dehumidification when the home is occupied and +60^F outdoor dew points. Locating a whole house 70 pint per day dehumidifier, an Ultra-Aire 70H in the basement alongside the heat pump would be the perfect combination for >50%RH throughout the home including the basement, regardless the cooling load or oversizing of the heat pump. This also provides <50%RH with the cooling off when the home is unoccupied and high outdoor dew points. This will be a big energy saver.
    Regards TB
    Regards TB
    Dec 2010
    Very good point. I had forgotten about that little issue.
    Sep 2009
    Arnold mo
    You need to get an energy audit and find out if your home has a lot of air leakage and any insulation issues. Heat pumps are lousy at providing comfort in winter in a home with a lousy envelope.
    An answer without a question is meaningless.
    Information without understanding is useless.
    You can lead a horse to water............
    http://www.mohomeenergyaudits.com
    Jul 2013
    All the duct work will be updated to R8. There will be 1 additional return added and 1 supply added for the larger unit. When I look at the AHRI certificates, the 3 ton unit is rated at 22,200BTUH @ 17 degree's F, the 4 ton unit is rated at 29,800BTUH @ 17 degree's F, both for region IV. Do you think the 7600 extra BTU from the 4 ton justifies going with the larger unit?
    If it gets your heating balance point to 25 or lower it is.
    Must be a big room that never heated or cooled right. That adding only one supply will gt you the proper air flow. 400 CFM additional supply to only one room?
    As recommended have an energy audit performed and adjust the load to allow a smaller unit to be used and save money in utility bills and be comfortable.
    Aug 2012
    North Dakota
    what duct work comes with ele. base board why not install a gas \ propane furnace ? for your climate youll be happier$