    York YT never seems to ramp down

    Hey guys,

    I have a York YT R-123 chiller with a VSD on it. It always seems to be running at 60 Hz with the prerotation vanes at 0% open despite never having to carry a load over ~60% FLA (49-51% at the time of this posting). Oddly now, I created a trend on the Optiview Control Center for the FLA and Hz and they're both been reading 0 all day... Is something not communicating internally and it's just running on some sort of default or limp mode? Is it normal for them to run at 60Hz no matter what?

    Current run conditions at the time of this posting:
    OA temp 77.6
    OA humidity 92.3%

    CW supply to chiller 76.0
    CW return to tower 79.6
    sat temp 80.8
    Cond press 14.1

    CHW supply to AHUs 44.0
    CHW return chiller 49.5
    sat temp 40.7
    evap press 5.6
    CHW set point 44.1

    FLA% 49
    Hz 60

    Chiller model number: YTG1A4E1-CNJ
    Serial number: GFLM 132473
    Drive model number VSD351 T-46

  2. #2
    Join Date
    Aug 2013
    Posts
    5
    Post Likes
    This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.

    You can find the rules for posting and qualifications here.

    Additional infractions may result in loss of posting privileges.
    Last edited by jpsmith1cm; 09-02-2013 at 09:40 PM.

  3. #3
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,675
    Post Likes
    BP420


    This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.

    You can find the rules for posting and qualifications here.

    Additional infractions may result in loss of posting privileges.



Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.