    manitowoc wont go into freeze

    Under counter unit QD0132a won't go into freeze . original complain was low ice production. Adjusted itp . turned it off to check flow valve . turned back on . now won't freeze . only water pump would be on . bin light would cycle on and off manually.. have very limited experience with ice makers . any help would be greatly appreciated..

  2. #2
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    4,512
    Low production is usually related to water issues, dirty machine, high head, or possibly a low charge/txv issue. Were there any error codes when you turned the unit back on? Compressor won't come back on because bin switch is not closed.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them

  3. #3
    Join Date
    Aug 2011
    Location
    silver spring md
    Posts
    26
    No codes . I looked many many times . but the bin light would cycle on and off when I move the damper . checked all electrical connections already. Will go back to clean the machine + check on bin switch again . thanks 2sac

  4. #4
    Join Date
    Aug 2011
    Location
    silver spring md
    Posts
    26
    No codes . I looked many many times . but the bin light would cycle on and off when I move the damper . checked all electrical connections already. Will go back to clean the machine + check on bin switch again . thanks 2sac

  5. #5
    Join Date
    Aug 2011
    Location
    silver spring md
    Posts
    26
    Put in new bin switch . fires right up . but how did it fail because I turn it off ?anyway , its working . watch it made 4 batches after I gave it a clean . thanks again 2sac .

  6. #6
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    4,512
    They just go bad. No rhyme or reason. Was the magnet on the curtain dirty? That could have been causing it to act up as well.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them

  7. #7
    Join Date
    Aug 2011
    Location
    silver spring md
    Posts
    26
    Magnet wasnt too bad . I got it going b4 I clean it