    Freezer upright will not reach temp,high superheat

    Have a 3 door upright victory giving me fits, r-404, inside temp 85,box 65 deg, pressures 16 and 340, superheat 100, cap tube system, system goes to 16 with warm box, high side was blowing off on internal relief, recovered a little gas
    No model on unit anywhere, do not know how much refrigerant suppose to be in it
    Have 12 oz in system,condenser clean,amp draw full load, new compressor,
    Thinking I have moisture or cap tube pug

  2. #2
    Join Date
    Jan 2010
    Location
    Vancouver Island
    Posts
    380
    Sounds like plugged dryer or cap tube.

    Sent from my SGH-I747M using Tapatalk 2

  3. #3
    Join Date
    Oct 2004
    Location
    Central WA
    Posts
    1,554
    Check for the nameplate inside the freezer, top left of the box near the front. Likely a plugged cap tube, probably killed the original compressor, and whoever replaced it overcharged to compensate. These are an easy conversion to txv.

  4. #4
    Join Date
    Mar 2013
    Location
    swan valley idaho
    Posts
    728
    340 head is to high. Clean coil well, check sub cooling. If you are restricted subcool will be high