    Jan 2011
    Freezer upright will not reach temp,high superheat
    Have a 3 door upright victory giving me fits, r-404, inside temp 85,box 65 deg, pressures 16 and 340, superheat 100, cap tube system, system goes to 16 with warm box, high side was blowing off on internal relief, recovered a little gas
    No model on unit anywhere, do not know how much refrigerant suppose to be in it
    Have 12 oz in system,condenser clean,amp draw full load, new compressor,
    Thinking I have moisture or cap tube pug
    Jan 2010
    Sea to Sky
    Sounds like plugged dryer or cap tube.
    Sent from my SGH-I747M using Tapatalk 2
    Yakima, WA
    Check for the nameplate inside the freezer, top left of the box near the front. Likely a plugged cap tube, probably killed the original compressor, and whoever replaced it overcharged to compensate. These are an easy conversion to txv.
    Mar 2013
    swan valley idaho
    340 head is to high. Clean coil well, check sub cooling. If you are restricted subcool will be high