    Trane RTU issue

    Model: YSC092A3ELA13D

    Cannot figure this thing out. No cooling call. Turned unit on and fan would come on and both compressors would come on then turn off. Gauged up, found high head pressure, washed the condenser good. Head pressure came down and started running and cooling for about 20 minutes. took the cover away to take gauges off and the damn thing turned off again and never would come back on. Started checking for an intermittent HPCO issue but found none. Bypassed every pressure cutout to see if they were causing the issue, no luck. Also bypassed freeze stat to see if it was opening. No luck. Now all it does is jog the blower when I apply power for a second or 2 and then nothing. What am I missing here? I didn't see anything else on the barely readable schematic that would cause the contactors to shut off. Any suggestions? Thanks in advance my friends.

  2. #2
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    How long is never? ASD delays in both the tstat and rtu could be your problem.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  3. #3
    Join Date
    Oct 2011
    Location
    Austin, TX
    Posts
    224
    Post Likes
    Thread Starter
    Every 5 minutes or so it would try to kick on but would immediately shut off the blower motor. I usually only work on refrigeration systems. Not up to speed with these trane units. Tech support is hard to get a hold of.

  4. #4
    Join Date
    Aug 2012
    Posts
    3
    Post Likes
    air proving switch on blower? revg62

  5. #5
    Join Date
    Aug 2004
    Location
    San Antonio TX Area
    Posts
    16
    Post Likes
    Will it run in "Test Mode" ??

  6. #6
    Join Date
    Aug 2004
    Location
    San Antonio TX Area
    Posts
    16
    Post Likes
    Hope it's allowed to post this since your diagram is not readable......

    From Trane:

    Simply place a jumper between Test 1 and Test 2 terminals on
    the Low Voltage Terminal Board and the unit will walk through its
    operational steps.

  7. #7
    Join Date
    Oct 2012
    Location
    Corryton,TN
    Posts
    73
    Post Likes
    I had one at a furniture store doing the same thing.one of the low voltage fuses was loose in the holder. It would wiggle itself open. try to keep it simple.

  8. #8
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    ALL of the screws in the TB 1 strip have to be tight. The test screws won't work correctly if they are loose, and the safeties are wired through the others.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •