    Had a tech top off a 410 unit with a pound or two of 22. Is it ok to just recover, flush lines, vacuum and recharge? Surely we don't need to replace equipment, right?
    Jan 2010
    Refrigerant for stationary equipment does not come with oil in it. That being said there would be no oil cross contamination. Always replace the filter when you open a system.
    May 2005
    Indianapolis, IN
    Good point about the refrigerant having no oil in it.
    Sounds like we will go with plan A then.
    Apr 2008
    maryland
    Happens to the best if us. Mine was a overtime call at 1am
    Sent from my SCH-I535 using Tapatalk 2
    IRELAND
    Id just change the gas . r22 has no problem mixing and running with poe oil ,Its the 410 that wont mix with the 22s mineral oil
    Feb 2012
    Pacific Northwest
    You're right that a R22 system has no problem with POE oil. But this was a 410 system adding R22 to it.
    Apr 2013
    Independence, MO
    You are sure right when you say it happens to the best of us! A 1 hr call turn into 6.
    Feb 2012
    Pacific Northwest
    Quote Originally Posted by JKerch View Post
    You're absolutely right about that one! I have tried to explain that to our relatively new service dispatcher. She has no comprehension of exactly what the difference between a maintenance call and a repair is.
    For example, last week I had to do a leak search, which I told her might take a few hours, and here she goes and schedules three more call in between. Maintenance calls no less!
    IRELAND
    Quote Originally Posted by HotWaterHeat View Post
    ya i know its a 410 was just saying no real need to flush as there be no sludge or anything formed as the 22 would mix ok
    Can anyone provide documentation as to this "sludge" that you're alleging that forms when PolyolEster oil and Mineral oil mix?
    Yes, I know that it is "common knowledge" that it happens, but I've got a problem with it.
    See, I've SEEN POE and mineral oil mixed with no problems. I've done it on instructions from customers and engineers intentionally.
    So, can anyone document it? Or are we just repeating the same old tales without spending any time to verify the truth of it?
    As to the original problem, pull the mixed gas and charge it up with new. Good to go.
    Refrigerant doesn't affect the oil. Doesn't matter if you put 22 in a 410a system or the other way 'round.
    IRELAND
    Good point could be an old wives tale but id prefer to be careful than to be caught.
    More like "common misinformation" from people who heard it from someone who heard it from someone who misunderstood something in a training class he was sleeping through.
    Mineral and POE oil are completely compatible with each other.
    RSES Certificate Member
    RSES-SWRA President
    Jun 2001
    So as long as there is no burnout you can use R22 lineset without flushing when converting the system to R410a? No need to worry about "R22 oil" in the old lineset?