Results 14 to 17 of 17
    Jan 2005
    Houston TX
    If you 78K hours run time without a starter Overhaul you need one. You should be able to go into the "service test" menu and check each individual contactor. If the starter has gone to "open" transition (the transition resister are no longer in the starter configuration, make sure either it stays online or leave it off. This type of operation will cause bearing damage if not addressed. See if the coils are getting the 120 volt signal and the delay is in the contactor pulling in. I have done this with 120 volt clip light on all 4 coils. If the transition contactor is working it will only be a blink or 1 second at the most. Also are you sure the screw is 100% unloaded ? good luck- GEO
    Having sex is like playing cards, if you don't have a good partner, you better have a good hand. !!!!!!
    dania,fl
    screwit
    can you please send me rthb-sb5
    ck33004@comcast.net
    ty
    up in the hizzy
    here
    Attached Files Attached Files
    Jul 2013
    Illinois
    It's after the why or start is engaged, soon as it disengages there is approx 2 second delay before delta kicks in.