  1. #14
    Join Date
    Jan 2005
    Location
    Houston TX
    Posts
    876
    If you 78K hours run time without a starter Overhaul you need one. You should be able to go into the "service test" menu and check each individual contactor. If the starter has gone to "open" transition (the transition resister are no longer in the starter configuration, make sure either it stays online or leave it off. This type of operation will cause bearing damage if not addressed. See if the coils are getting the 120 volt signal and the delay is in the contactor pulling in. I have done this with 120 volt clip light on all 4 coils. If the transition contactor is working it will only be a blink or 1 second at the most. Also are you sure the screw is 100% unloaded ? good luck- GEO
    Once in a while everything falls into place and I am able to move forward, most of the time it just falls all over the place and I can't go anywhere-GEO

  2. #15
    Join Date
    Sep 2008
    Location
    dania,fl
    Posts
    30
    screwit
    can you please send me rthb-sb5

    ck33004@comcast.net

    ty

  3. #16
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    1,392
    here
    Attached Files Attached Files

  4. #17
    Join Date
    Jul 2013
    Location
    Illinois
    Posts
    33
    It's after the why or start is engaged, soon as it disengages there is approx 2 second delay before delta kicks in.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event