    Apr 2013
    South of Oklahoma
    Trane purifier purge alarm
    I have a York YT chiller that is equipped with a Trane purifier purge. Model number of purge starts is PRGC. I'm getting a "purge is misconfigured as unit mounted" alarm. I can't find in the purge manual where this is configured. I'm assuming I have a software problem, but would appreciate any help I can get.
    Aug 2009
    Prattville, Alabama
    It's been a while, and I'm working from memory here, but try going into "Settings". There are just a few items, and one of them gives you a choice between "Unit Mounted" and "Standalone". You want to select "Standalone". If I'm wrong, hopefully someone will be along shortly. This does have the UCP2 style control panel, right?
    Aug 2009
    Prattville, Alabama
    Hmmm, I just found my IOM, and it doesn't mention this after all. Try powering down the purge, and then power it back up. I seem to have heard of this alarm before, but I don't think I've seen it myself. I'll keep giving it some thought...
    Apr 2013
    South of Oklahoma
    This one has an older style panel that doesn't have a "settings" button. But I believe I figured it out. The J1 jumper must have had a loose connection at the plug. When I tinkered with it I would get the fault. I appreciate the quick response.
    Aug 2009
    Prattville, Alabama
    Try verifying good, clean wiring connections between the "Human Interface Panel" and the purge module.
    Aug 2009
    Prattville, Alabama
    Oops, beat me to it. Good job.