First what temp is it set at?
Second sounds like a perfectly sized system. Welcome to the real world.
Stat finally gets satisfied when the sun starts to drop off (7 pm ). I have cathedral ceilings (15'-6")in living room, din room & east exposure.
The house Is about 50 years old. Living room& din room is apprx 450 sq ft and I'm dumping in about 750 cfm's. supply wall grilles(3) are at 9'-0 & return is a sidewall about 11'-0 center line(16 x 30 ). I also have a 30 x14 return ceiling grille in the center hallway on a 8'-0 ceiling. House floor plan is about 1100 sq ft. Why does this unit keep running during these high heat days ? I was thinking is it the cathedral ceilings with very old insulation?
Please help
First what temp is it set at?
Second sounds like a perfectly sized system. Welcome to the real world.
That's what it's supposed to do.
insulation doesn't stop performing as it ages.
50 years ago we didn't invest a lot in insulation, so it
may not be recommended R-values for today.
long run times of hvac isn't a bad thing, it is the short
cycling that cost you to operate the system, lessens
dehumidification & shortens life of the system.
here in hot humid La. correctly sized units can run pretty
much non stop from 2 pm until 9 pm.
just fyi.
is there a comfort or high utility cost problem??
750 cfm for 450 sq ft area is a lot of cfm...almost 2 tons.
do you need that much air to cool that area<<
what size unit for 1100 sq ft?
what location?
best of luck.
The cure of the part should not be attempted without the cure of the whole. ~Plato
The closer to the sun you get without insulation the more heat transfer there will be. Just be glad it cycles at night.
Its not that big of an area. How about ripping the ceiling out and spray foam it.
Options:
1. Running
2. NOT running
3. Set t-stat = 82'F from 10:50 AM to 6:40 PM.
4. Have the sun not visit at all during July & August.
Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities
With high ceilings the main thing is to NOT disturb the air above 8 feet; because air above that point acts as insulation, as heat rises, so the lower temp difference between the warmer ceiling air area & the attic or roof areas is left alone.
You have a High Return that should NOT be there for either cooling or heating purposes, also supply diffusers should be lowered; could even be at the baseboards' area; the throw should be at the occupant level area but usually not directly at areas where occupants will be seated.
The idea is to just cool &/or heat the air that is at the level of the occupants; therefore, all the air above say 8' is left undisturbed as a barrier to temp-difference between the ceiling & the interior; you absolutely do NOT want to be cooling that upper area so that there won't be a large temp-difference which increases the rate of heat transfer.
That alone could make a big difference in your cooling load. Why cool all the warm insulation air nearest the ceiling you don't live in that area; or how is the rest of your home designed? That will affect what you do...
AOP Forum Rules:
Rules for Posting
Rules For Equipment Owners
Equipment Owners Find a Contractor HERE!
udarrell
the problem is that often, cathedral ceilings are adjacent to balcony upper floors... which do need cooling, so the cathedral also needs to be cooled. is this the case with your house as well?
The TRUE highest cost system is the system not installed properly...
Find a HVAC-Talk Contractor by clicking here
Click below to BECOME a pro member
https://hvac-talk.com/vbb/forumdispl...ip-Information
Do you go to a boat repairman with a sinking boat, and tell him to put in a bigger motor when he tells you to fix the holes?
I am yourmrfixit
No just a roof above this problem area. Sheetrock on the inside