    I blew the b comp today and need to make it so a will run, only prob is that all the b alarms shut it down. How do I do this in the controls.

  2. #2
    Join Date
    Feb 2012
    Location
    utah
    Posts
    106
    Post Likes
    Thread Starter
    Sorry I was in a hurry, I need to get comp a to run but all the alarms shut down the circuit. Is there a way to make it so comp b never tries to start? It is a rtaa270 with adaptive control

  3. #3
    Join Date
    Oct 2010
    Location
    Greece
    Posts
    47
    Post Likes
    Hi,
    If in A! circuit you have 2 compressors, a fault from one compressor stops also the other.
    You cannot start only one compressor and it is not good to start it if the other one is burned out.
    It is possible if you make a lot of changes in control cables and programming but it is not recommended.
    You should only run B! circuit.
    Regards,
    CV

  4. #4
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    2,838
    Post Likes
    Quote Originally Posted by nique View Post
    Sorry I was in a hurry, I need to get comp a to run but all the alarms shut down the circuit. Is there a way to make it so comp b never tries to start? It is a rtaa270 with adaptive control
    There is a way to do it, go to service settings, look for compressor "b" "unlock" and change it to "lockout", press "next" then "enter" and you are good to go.

  5. #5
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    1,884
    Post Likes
    Quote Originally Posted by valdelocc View Post
    There is a way to do it, go to service settings, look for compressor "b" "unlock" and change it to "lockout", press "next" then "enter" and you are good to go.
    If you have a compressor failure you need to do more than simply letting the controls lock it out. You need to physically disconnect the compressor leads. If the chiller has the Cutler Hammer contactors, you can remove the contactor head.

  6. #6
    Join Date
    Feb 2012
    Location
    utah
    Posts
    106
    Post Likes
    Thread Starter
    I read that manual for half the night and never saw a thing for compressor lockout, what p# is it?

  7. #7
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    1,884
    Post Likes
    Quote Originally Posted by nique View Post
    I read that manual for half the night and never saw a thing for compressor lockout, what p# is it?
    P1A
    IOM 3 page 94. That's for circuit lockout, there is no compressor lockout but since this chiller has only 1 compressor per circuit, circuit lockout will do.

  8. #8
    Join Date
    Feb 2012
    Location
    utah
    Posts
    106
    Post Likes
    Thread Starter
    That's the problem circuit 1 has two comp. "A" is a 100 ton and "B" is a 70 ton. Circuit 2 has "C" which is a 100 ton. I've taken "B" completely out of the circuit but the controls don't know that. The readout is before the one with next and enter. Just the up, down and side arrows.

  9. #9
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    1,884
    Post Likes
    Quote Originally Posted by nique View Post
    That's the problem circuit 1 has two comp. "A" is a 100 ton and "B" is a 70 ton. Circuit 2 has "C" which is a 100 ton. I've taken "B" completely out of the circuit but the controls don't know that. The readout is before the one with next and enter. Just the up, down and side arrows.
    Ok, I thought it was a 170 ton as per your 1st post but in your 2nd post, you said 270 ton. The only thing you can do is create a compressor alarm such as making the oil pressure switch show tripped and that compressor will lock out in alarm but you need to also physically disconnect the power wiring at the contactor (or pull the contactor head) so there is no way the compressor can start.

  10. #10
    Join Date
    Feb 2012
    Location
    utah
    Posts
    106
    Post Likes
    Thread Starter
    I've taken the compressor out both refrigerant and electrical. But when any alarm for that compressor comes up the whole circuit drops. I tried the oil switch with the same result. Any other ideas?

  11. #11
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    2,838
    Post Likes
    Have you tried changing the number of compressors in the "machine configuration" menu?

  12. #12
    Join Date
    Feb 2012
    Location
    utah
    Posts
    106
    Post Likes
    Thread Starter
    I did, also stages.

  13. #13
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    2,838
    Post Likes
    Well, its time to take a drive to your local Trane office and have them call chiller tech support, make sure to bring some Snickers. .....and please let me know the rest of the story!