Results 1 to 20 of 20

Thread: HVAC Repair Second Opinion

  1. #1
    Join Date
    Jul 2013
    Posts
    6
    Post Likes

    HVAC Repair Second Opinion

    Name:  20130714_081632.jpg
Views: 951
Size:  63.2 KBName:  20130714_081619.jpg
Views: 818
Size:  59.8 KBI'm probably bordering on DIY here (because I'm second guessing someone's work) -- and I did read the rules -- however what I'm looking for is do I need to call in a second contractor?

    The gist...

    Blower relay out on control board (Bryant 350MAV). Dayton, OH contractor comes out and jumpers the blower motor so we at least have AC in the house during July. Comes back with relay and hooks up. I'm going to try and upload some pictures.

    Questions.

    1) Is this standard to leave the board hanging down by the blower housing not mounted to anything?
    2) Is this a standard fix to bring my two speed system down to a one speed (only black wire hooked up, not yellow, red, blue, etc. I understand two of them are unused spares)
    3) Could he have bypassed any of the safety features of the control board by doing this?
    4) The 115AC is just hanging there and nearly touching the blower door when closed, seems like a safety concern.

    Sorry my questions are really centered around safety and if I need to call them back because this was not an industry standard repair.....if so then I'll just shut up and just assume I'm out-of-my-league and tuck my tail between my legs.

    VR

    JHUFlyerName:  20130714_081619.jpg
Views: 818
Size:  59.8 KBName:  20130714_081632.jpg
Views: 951
Size:  63.2 KB

  2. #2
    Join Date
    Apr 2010
    Location
    Winnipeg,Manitoba,Canada
    Posts
    176
    Post Likes
    get a qualified contractor to come look at what you have there.
    hard to tell if all or only some wires should be hooked up.
    that seaquancer should be mounted.

  3. #3
    Join Date
    Sep 2004
    Location
    Memphis
    Posts
    2,502
    Post Likes
    I can see doing that on the weekend, but id just pay to have the board replaced and have it done right.
    Life is like a jar of jalapenos. What you do today might burn your ass tomorrow.

  4. #4
    Join Date
    Jul 2013
    Posts
    6
    Post Likes
    Thread Starter
    The guy who put the sequencer on their was a qualified HVAC technician. I'm usually not into second guessing peoples work; however, I like to be an informed consumer. But your professional opinion is very appreciated (helps me formulate this may not have been an "A-team" repair). And this was done on the contractor's second call out. The first time he just jumper'ed the fan to the blower safety switch.

    The guy was very nice and explained what he was doing; however, I'm an aircraft mechanic and it bothered me to see that relay thing not mounted to something. Again, if what he did is industry standard than I am just expecting too much.

  5. #5
    Join Date
    Oct 2012
    Location
    Wisconsin
    Posts
    6,676
    Post Likes
    Did they give you an option of replacing the board?

    What they did is substandard to say the least. Even as a temporary repair at the least they should have mounted/anchored that sequencer (thing with all the wires hanging down). Also what kind of heat do you have? If its gas heat the board is what turns on the fan during the heating season, so your heat won't work if gas.

  6. #6
    Join Date
    Jul 2013
    Posts
    6
    Post Likes
    Thread Starter
    Mike19. Yes it's gas forced air. I would try the heat just to check, but it's 90 outside and the wife would not be happy. And no there wasn't an option; however, I thought that's what they would do.

  7. #7
    Join Date
    Oct 2011
    Location
    Culver, Oregon (Central OR)
    Posts
    5,051
    Post Likes
    This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.

    You can find the rules for posting and qualifications here.

    Additional infractions may result in loss of posting privileges.
    Last edited by jpsmith1cm; 07-14-2013 at 10:01 PM.

  8. #8
    Join Date
    Dec 2011
    Location
    Katy, TX
    Posts
    255
    Post Likes
    This is a hack job if not repaired properly. That board needs to be replaced with a Carrier/Bryant factory authorized control board. You should demand having the component replaced. But be prepared to pay a good price for it. .
    Last edited by Dad; 07-15-2013 at 09:29 AM.

  9. #9
    Join Date
    Jul 2010
    Location
    wisconsin
    Posts
    270
    Post Likes
    Quote Originally Posted by jhuflyer View Post
    Name:  20130714_081632.jpg
Views: 951
Size:  63.2 KBName:  20130714_081619.jpg
Views: 818
Size:  59.8 KBI'm probably bordering on DIY here (because I'm second guessing someone's work) -- and I did read the rules -- however what I'm looking for is do I need to call in a second contractor?

    The gist...

    Blower relay out on control board (Bryant 350MAV). Dayton, OH contractor comes out and jumpers the blower motor so we at least have AC in the house during July. Comes back with relay and hooks up. I'm going to try and upload some pictures.

    Questions.

    1) Is this standard to leave the board hanging down by the blower housing not mounted to anything?
    2) Is this a standard fix to bring my two speed system down to a one speed (only black wire hooked up, not yellow, red, blue, etc. I understand two of them are unused spares)
    3) Could he have bypassed any of the safety features of the control board by doing this?
    4) The 115AC is just hanging there and nearly touching the blower door when closed, seems like a safety concern.

    Sorry my questions are really centered around safety and if I need to call them back because this was not an industry standard repair.....if so then I'll just shut up and just assume I'm out-of-my-league and tuck my tail between my legs.

    VR

    JHUFlyerName:  20130714_081619.jpg
Views: 818
Size:  59.8 KBName:  20130714_081632.jpg
Views: 951
Size:  63.2 KB
    Its sad that the contractor didnt have that board in stock on his van, i carry two of these factory boards on my van he spent more time dinking with the relay than just replacing the board . No need to use a sequencer either, he should have used a simple rib relay and fastened it to a knockout hole and wire nutted it properly. Is this contractor a carrier or bryant dealer?

  10. #10
    Join Date
    Dec 2007
    Posts
    13,231
    Post Likes
    What a JOKE!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!

    There is a far easier way to do a temporary repair on that unit.

    The picture of the "board" as you call it is nothing more than a rip off of your money!!!! It's not a repair, it's stupidity at its finest.

    Call his boss and show them these photos. If this is what passes for a proper repair, run as fast as you can to the next unqualified technician!!!!

    This is NOT a 2 stage or speed system. You have a speed used for heat and another(usually higher) for a/c.
    The Food Stamp Program, administered by the U.S. Department of Agriculture, is proud to be distributing the greatest amount of free meals and stamps EVER.
    Meanwhile, the National Park Service, administered by the U.S. Department of the Interior, asks us to "Please Do Not Feed the Animals". Their stated reason for this policy "... the animals become dependent on handouts and will not learn to take care of themselves."
    from an excerpt by Paul Jacob in Sun City, AZ

  11. #11
    Join Date
    Jul 2013
    Posts
    6
    Post Likes
    Thread Starter
    Quote Originally Posted by pacnw View Post
    What a JOKE!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!

    There is a far easier way to do a temporary repair on that unit.

    The picture of the "board" as you call it is nothing more than a rip off of your money!!!! It's not a repair, it's stupidity at its finest.

    Call his boss and show them these photos. If this is what passes for a proper repair, run as fast as you can to the next unqualified technician!!!!

    This is NOT a 2 stage or speed system. You have a speed used for heat and another(usually higher) for a/c.
    My apologies for calling it multi-speed; I knew it definitely wasn't a variable speed. Thank you for professional opinion everyone, looks as though I am learning the hard way; through my pocketbook.

  12. #12
    Join Date
    Sep 2003
    Posts
    1,695
    Post Likes
    First and foremost I wouldn't do it this way. It seems poorly done

    I just did this for a customer actually who had a power surge during a recent and very severe
    Thunderstorm.

    I got the call at 4:30 on 10th and since it was a service contract I was there that evening and it had a bad transformer and a bad board. I wired in a new transformer and bypassed the board and got them a/c for the night.

    The next day I called the local Bryant Carrier Distributor ordered a board and went back out and replaced the board
    and corrected the wiring changes made made sure the furnace worked in cool, heat and fan only.

    I would call the company that did the repair and ask to speak to the boss.

    I would ask him if this is just a temporary repair because it doesn't seem very safe with the part just hanging there and you are concerned about there being a potential fire or electrical shock issue and see what he says.

    And then I would act accordingly.

    Either having them properly repair the furnace by replacing the board with the factory replacement or have someone else out to do it properly.

  13. #13
    Join Date
    Dec 2011
    Location
    Katy, TX
    Posts
    255
    Post Likes
    Quote Originally Posted by small change View Post
    First and foremost I wouldn't do it this way. It seems poorly done

    I just did this for a customer actually who had a power surge during a recent and very severe
    Thunderstorm.

    I got the call at 4:30 on 10th and since it was a service contract I was there that evening and it had a bad transformer and a bad board. I wired in a new transformer and bypassed the board and got them a/c for the night.

    The next day I called the local Bryant Carrier Distributor ordered a board and went back out and replaced the board
    and corrected the wiring changes made made sure the furnace worked in cool, heat and fan only.

    I would call the company that did the repair and ask to speak to the boss.

    I would ask him if this is just a temporary repair because it doesn't seem very safe with the part just hanging there and you are concerned about there being a potential fire or electrical shock issue and see what he says.

    And then I would act accordingly.

    Either having them properly repair the furnace by replacing the board with the factory replacement or have someone else out to do it properly.
    If you don't get a satisfactory response from the owner, PLEASE make the necessary reports to Better Business Bureau, Angie's List, ext... This is how the professionals rise to top and the HACKS are pushed out!

  14. #14
    Join Date
    Dec 2011
    Location
    Northwest Georgia
    Posts
    111
    Post Likes
    If that was an aircraft would you fly in it? I sure wouldn't.

  15. #15
    Join Date
    Feb 2012
    Location
    Ohio
    Posts
    261
    Post Likes
    Wow. Just replace the board with a OEM board and be done with it. That isn't even a good temporary fix.

  16. #16
    Join Date
    Mar 2009
    Location
    Mount Holly, NC
    Posts
    9,064
    Post Likes
    nope, not standard practice, not normal, not safe, and not recommended!

    I love how all the spare speed wires are just stuffed up into the wire bundle, ready to fall and short onto something... you've only got high speed... it's gonna be drafty come winter time, if the heat even comes on!
    The TRUE highest cost system is the system not installed properly...

    Find a HVAC-Talk Contractor by clicking here

    Click below to BECOME a pro member
    https://hvac-talk.com/vbb/forumdispl...ip-Information

    Do you go to a boat repairman with a sinking boat, and tell him to put in a bigger motor when he tells you to fix the holes?

    I am yourmrfixit

  17. #17
    Join Date
    Jul 2013
    Posts
    6
    Post Likes
    Thread Starter
    I appreciate everyone's responses. I have another company coming out to complete the job, the other company won't even send me an invoice. Thank you again for everyone's expertise.

  18. #18
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by 37bluebird View Post
    Wow. Just replace the board with a OEM board and be done with it. That isn't even a good temporary fix.
    37bluebird

    Please review the AOP Forum rules found here.



  19. #19
    Join Date
    Dec 2007
    Posts
    13,231
    Post Likes
    Quote Originally Posted by jhuflyer View Post
    I appreciate everyone's responses. I have another company coming out to complete the job, the other company won't even send me an invoice. Thank you again for everyone's expertise.
    They should not expect payment for that (insert your description here)!

    Did they even want to hear/see what was done?

    If an invoice does come, keep photos and refuse to pay it.
    The Food Stamp Program, administered by the U.S. Department of Agriculture, is proud to be distributing the greatest amount of free meals and stamps EVER.
    Meanwhile, the National Park Service, administered by the U.S. Department of the Interior, asks us to "Please Do Not Feed the Animals". Their stated reason for this policy "... the animals become dependent on handouts and will not learn to take care of themselves."
    from an excerpt by Paul Jacob in Sun City, AZ

  20. #20
    Join Date
    Jun 2007
    Location
    Round Rock
    Posts
    4,744
    Post Likes
    So that was the "permanent" fix? That's hilarious. I might do something like this to get them cooling, but never call it fixed like that. I would actually hot wire the motor to run all the time and the condenser would cycle on and off. This way you won't decide yourself that's its fixed and not call me back out to fix permanently. With the fan running all the time, it will irritate you enough to make sure I get invited back to fix it with correct board.
    I like DIY'ers. They pay better to fix.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •