Page 2 of 3 FirstFirst 123 LastLast
Results 14 to 26 of 32
  1. #14
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,541
    Post Likes
    Yes, but how did it get overcharged? How has a 2007 model unit ran this long flooding? Is evap dirty?

  2. #15
    Join Date
    Sep 2012
    Location
    thomaston, ct
    Posts
    371
    Post Likes
    Thread Starter
    The return was so small it was almost vacuuming all of the dust out of the house. When I first went there the filter was really bad and struggling for air and that's why we added the returns.

    I'm not sure if whoever worked on the unit previously might have added thinking the charge was low trying to bring up the evap saturation temp.

    I also foaming cleaned the evap coil and the condensor.

    I will bring the reclaimer there and try and pull the unit down. At that point I might as well change the filter drier and check the orifice.

    He says since the second year of operation the compressor has been making the noise progressively worse.

  3. #16
    Join Date
    Jul 2013
    Posts
    63
    Post Likes
    Damage may be done.

  4. #17
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    9,134
    Post Likes
    Quote Originally Posted by jlanesey View Post
    The air handler is fixed orifice. I need to charge to superheat right? And how many degrees superheat would be an acceptable starting point?
    Yes.

    Send me an email(address is in my profile), and I will get you a superheat charging chart.
    Instead of learning the tricks of the trade, learn the trade.

  5. #18
    Join Date
    Sep 2012
    Location
    thomaston, ct
    Posts
    371
    Post Likes
    Thread Starter
    He is ready to cut everything out and install new a/h and condensor. I'd rather fix it though. I can't see spending a couple grand when it could be a minor problem. The compressor may even still be under warranty.

  6. #19
    Join Date
    Jan 2010
    Location
    Sea to Sky
    Posts
    2,080
    Post Likes
    I was looking at your pictures of the Goodman build sheet. I see a model number across the top. Then the items circled. I am a little confused why the 36 for a 3ton unit is circled when there is a 24 indicating a 2 ton unit in the model number up top.

    Is it a 3 ton air handler or a 2 ton air handler? The condensing unit appears to be a 3 ton, so if you have a 2 ton air handler....gonna have some issues....

  7. #20
    Join Date
    Sep 2012
    Location
    thomaston, ct
    Posts
    371
    Post Likes
    Thread Starter
    Quote Originally Posted by BALloyd View Post
    I was looking at your pictures of the Goodman build sheet. I see a model number across the top. Then the items circled. I am a little confused why the 36 for a 3ton unit is circled when there is a 24 indicating a 2 ton unit in the model number up top.

    Is it a 3 ton air handler or a 2 ton air handler? The condensing unit appears to be a 3 ton, so if you have a 2 ton air handler....gonna have some issues....
    Woah! Good catch! Didn't even notice that. I'm gonna go tommorrow and look at the plate on the unit and see if that matches the top number.

  8. #21
    Join Date
    Feb 2013
    Location
    Sonora, California, United States
    Posts
    3,971
    Post Likes
    have you figured out why the refer looked red? does it smell right? I dont know what all colors dye come in but maybe someone else charged and added dye?

  9. #22
    Join Date
    Apr 2010
    Location
    working overtime
    Posts
    867
    Post Likes
    Quote Originally Posted by rundawg View Post
    Yes.

    Send me an email(address is in my profile), and I will get you a superheat charging chart.
    Would it be possible for me to get one of those. Charts I have been looking for one and cannot find it.

  10. #23
    Join Date
    Sep 2012
    Location
    thomaston, ct
    Posts
    371
    Post Likes
    Thread Starter
    Quote Originally Posted by cavalieri85 View Post
    Would it be possible for me to get one of those. Charts I have been looking for one and cannot find it.
    Those charts are great, thank you!

  11. #24
    Join Date
    Sep 2012
    Location
    thomaston, ct
    Posts
    371
    Post Likes
    Thread Starter
    He sent me this picture this morning. Condensor literature clearly states txv only. Could this also be an issue?

    Name:  ImageUploadedByTapatalk1373891044.701823.jpg
Views: 213
Size:  82.1 KB

    Also he observed yesterday that the short cycling startup, Hp switch, normal cycle only happens when it's above 80 outside.

    I'm going to go there again today and try to properly check the charge and go from there.

  12. #25
    Join Date
    Sep 2012
    Location
    thomaston, ct
    Posts
    371
    Post Likes
    Thread Starter
    Quote Originally Posted by BALloyd View Post
    I was looking at your pictures of the Goodman build sheet. I see a model number across the top. Then the items circled. I am a little confused why the 36 for a 3ton unit is circled when there is a 24 indicating a 2 ton unit in the model number up top.

    Is it a 3 ton air handler or a 2 ton air handler? The condensing unit appears to be a 3 ton, so if you have a 2 ton air handler....gonna have some issues....
    Also double checked the model number, air handler is definitely 3 ton.

  13. #26
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    9,134
    Post Likes
    Quote Originally Posted by cavalieri85 View Post
    Would it be possible for me to get one of those. Charts I have been looking for one and cannot find it.

    Check your email.
    Instead of learning the tricks of the trade, learn the trade.

Page 2 of 3 FirstFirst 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.