    Carrier rooftop unit - high suction, low head pressure
    Hi all,
    I'm new to this forum so I'd figured I would give it a shot.
    Today I repaired a leak on a unit and replaced the filter drier (leak on a fitting in the condenser). When I charged the unit with the factory charge of 7lb 8oz (as per nameplate) I began to check some Temperatures and pressures. I was receiving a suction pressure of 95psi and a head pressure of 180. I thought at first it was my compressor valves (tin can recip) so I covered my condenser coil and saw my pressure raise. So I new it wasn't my compressor, I checked the second stage which was working 2 weeks ago when I performed maintenance and it was having the same issue with the pressure. So the issue I believe is related between both stages.
    Here are a few numbers that might help
    Suction - 95psi
    Head pressure - 180psi
    10F over Evap coil (75-65F)
    5F over evap coil when running stages one at a time (75F-70F)
    10F superheat per stage
    No temperature rise over filter driers
    If ante has any idea that would be great.
    Feb 2011
    Sacramento, CA
    What type of metering device? How is the airflow across the evap? What's the sub cooling? Amp draw on each compressor?
    I have done so much with so little for so long, that now I can do almost anything with nothing at all.
    Salem, WI US
    I agree with Gocolts however you may want to verify your suction readings with another gauge if you haven't done so. The temps and pressure you indicate are a little strange. I am a summing the refrigerant is R22......
    Betabass
    Success is to be measured not so much by the position that one has reached in life as by the obstacles which he has overcome.
    Jul 2013
    Amp draw
    Compressor 1: 5.1
    Compressor 2: 5.3
    LRA: 5 (but they are both pumping so I find that kinda odd)
    Metering device: fixed Orfice
    Airflow:
    Condenser coil: single coil, fins straight, just cleaned it on maintenance
    Evaporator coil:
    Clean, brand new filters.
    Supply/return ducts: have not checked sizing as it has worked previously.
    Refrigerant: R22
    Also, what
    Jul 2013
    did you zero your gauges and was the economizer open
    Jul 2013
    Quote Originally Posted by andhereweare View Post
    I zero my gauges, and I checked them against another set, my economizer was closed.
    Jan 2010
    [QUOTE=Jordan615;16334291]
    LRA (locked rotor amps) 5
    Jul 2013
    [QUOTE=VTP99;16336051]
    Quote Originally Posted by Jordan615 View Post
    But if it was locked up wouldn't it not be pumping at all? Also if a compressor valve was gone wouldn't it lower my amp draw?
    I can't see both compressors being gone?
    Oct 2011
    Chicagoland Area
    Oct 2011
    Chicagoland Area
    [QUOTE=Jordan615;16336591]
    You probably meant RLA? You did not mention 2 things that may help, ambient and load.
    willowick ,oh
    i will go out on the chopping block and say you need new compressor. very low compression ratio and low super. Unless someone drilled out the orfices.When you blocked up the condenser section i bet the suction climbed right up with the head pressure didnt it.
    Jul 2013
    Quote Originally Posted by heresjohnnyb View Post
    No. The suction stayed roughly the same.
    With locked condenser(both stages reacted the same)
    Suction - 95psi
    Head pressure - 300psi
    Feb 2011
    Sacramento, CA
    In your original message you said your head pressure was 180, now it's 300? What is your sub cooling? I almost bet that it's high. What's the OSA temp?