Results 14 to 26 of 37
Thread: External Drier for Trane XL14I
04-14-2007, 01:33 PM #14
- Mar 2007
- 184
compressors were fine just a bad tech...1st problem was bad king valve...
2nd problem was loose fan motor on top since installer replaced plastic top with metal one due minimal clearance. < somehow Trane paid for replacement of 2 compressors on the same unit b/4 Trane came out and figured out problem >
04-14-2007, 01:42 PM #15
- Mar 2007
- 184
I forwarded the HACK's email to my Trane Territory Mgr for Phx plus the Field Service Rep for my account.
I explained I wanted it in writing I thought the contractor's email was BS.
Even my inside contact with the contractor says they screwed up but mgt has everyone on very short leashes and I suspect this screwup would cost em more money! (when they did the coil replacement I figured what 30 min/system to cut out the internal drier as they installed a new external drier)
04-14-2007, 01:44 PM #16
- Mar 2007
- 184
Being a dumb homeowner do Trane Territory Mgr for Phx have much power & what is a Trane Field Service Rep?
If I need to where do I escalate in Trane above them?
04-14-2007, 02:03 PM #17
Trane TM = sales person for Trane distributor
Trane FSR = technical representative for Trane distributor
Any letter or email sent to Trane corporate goes to consumer group. They answer you or forward to FSR for him to handle. While the FSR has a boss, the FSR is ultimately responsible to resolve your issues.Merry Christmas
04-14-2007, 03:19 PM #18
- Mar 2007
- 184
04-14-2007, 11:17 PM #19
Banned
- Aug 2002
- Office and warehouse in both Crystal River & New Port Richey ,FL
- 18,836
Yes, jr@bigorange.com lol
04-15-2007, 04:01 AM #20Merry Christmas
04-17-2007, 11:15 PM #21
- Mar 2007
- 184
Trane Internal Drier is not a Drier?
contractor just told me on my XL14I the Trane factory installed driers are not driers?
"driers that are in the system are strainers not filter driers"
Any XL14I experts out there? Is this more contractor BS and do these need to be cut out/removed during compressor replacement? ( see my original post below )
04-17-2007, 11:19 PM #22
- Mar 2007
- 184
Mark,
Are you saying there are 2 driers from the factory with the Trane XL14I?
Contractor is going to replace them I think but they are calling them "strainers" & not filter driers--are we referring to the same parts?
I emailed my FSR but did not get a reply as I suspect he responded to the contractor instead...
I did talk voice with my TM would said the contractor was talking BS on the contract being voided had they cut them out!
04-18-2007, 12:03 AM #23
Yes, there are 2 internal filter driers in your Trane heat pump. There is also a check valve, so refrigerant only goes through one at a time. One for heat mode, one for cooling mode.
They are definitely filter driers and not just strainers. If you cut one open, there are desiccant beads inside of it.
04-18-2007, 12:10 AM #24
- Mar 2007
- 184
04-18-2007, 12:24 AM #25
Yes
04-18-2007, 02:42 PM #26
- Mar 2007
- 184
Trane XL14I Filter Driers Replaced!
FINALLY...
Tech is onsite replacing my Trane XL14I Filter Driers (factory internal driers/strainers) and cut open 1 as he was always told they were just strainers--guess what he found?
Trane XL14I Filter Driers from the factory are of full desiccant beads inside so they are driers and not just a strainer.
My contractor was not aware of this even after I had my Trane TM & Trane FSR get involved--somehow they all still thought I was crazy till they cut them open.
Contractor thought they were protected since they always run with their own external filter driers on all installs? Not sure of the harm but if the factory drier isn't replaced during a compressor swap like they did for me?