Results 1 to 10 of 10
Thread: York piston
    Jul 2013
    Florida
    York piston
    The piston that comes with the york condenser. Is it necessary to install with the unit or is it only for certain occasions. Coil is matching.
    Have to see what piston the coil came with.
    Yakima, WA
    Yes. Install the piston unless you are converting to an expansion valve.
    Oct 2010
    Quote Originally Posted by cjpwalker View Post
    X2, the coils come with no piston installed, it comes with the outdoor unit install instructions, don't forget to put the valve stem in the external equilizer tap or you'll have a leaker...
    May 2011
    Western, KY
    It's necessary if your intention is to meter the refrigerant.
    The coils usually come with a screw on fitting, make sure the appropriate piston is installed when you screw the fitting on, same on the air handlers. They also come with a schrader core, there's a tap inside the coil on the suction line for if you're installing a txv equalizer tube, if not you're supposed to loosen the fitting, install the schrader core and put a cap or the fitting back on.
    May 2011
    Western, KY
    Quote Originally Posted by jtrammel View Post
    19 seconds too slow, knew I shouldn't have paused for a drink ; )!
    Jul 2013
    Florida
    The condenser paper work will tell me if the piston is right or the coil paper work? btw these are just coils on furnaces. No air handlers.
    Jul 2013
    Florida
    Also, coils come with a piston.
    Need to use the piston that the condenser needs. Piston in coil may or may not be the right size.
    Nov 2007
    Mississippi
    Use the piston (or flow rater) that came with condenser. FYI the nut you remove to swap piston is reverse threaded. At least they are on the older ones. I have not installed a new York in years.