    Honeywell wifi stats

    I installed my first wifi stat today. They only had a 4 wire ran to it. I tried using the green wire for the common. It seemed to work ok. The fan came on for both heat and air. I informed the homeowner that the fan only wouldn't work. Most people never use that anyway. Does anybody see any problem that might develop by doing this?
    Life is like a jar of jalapenos. What you do today might burn your ass tomorrow.

  2. #2
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,012
    No not really. Just test that the furnace energizes fan with a Y call because some don't.

  3. #3
    Join Date
    Dec 2004
    Location
    Grand Rapids, MI
    Posts
    611
    as long as you cycled heating & cooling and it operated properly = you are golden.
    most modern furnaces know you are running ac and the fan will turn "on".
    luck dan