    I recently installed a 2 ton, which was sized as, and am having a difficult time getting the space to cool down past 74.
    Long story short, air handler is in attic, condenser at ground level. air handler is txv, r-22, has sight glass and drier. i have tried to charge via sight glass, by feel of suction line, and superheat/subcooling (not efficient in either). i do not believe there is a receiver in unit.
    I once had same scenario a while back turned out was overcharged as i charged by sight glass.
    Thanks for the advise,
    Matt
    Southold, NY
    You got lucky with fixing your own fridge:
    http://hvac-talk.com/vbb/showthread....usehold-fridge
    Time to call a pro.
    Oct 2010
    You need to charge it to the manufactures subcooling, somewhere in the 8-12* range usually.
    Oct 2010
    AZ
    Charge by manufacturers specs as jtrammel said. Post SC, SH, pressures, refrigerant, air temp entering/leaving, and we will be better able to tell the problem.
    May 2013
    STP, MN
    I have a house fridge I am working on, actually is mine and am contractor but not very proficient in refrigeration
    Based on that, call a pro, you are going to hurt yourself or that unit
    Jun 2001
    If it's "recently installed" why is it R22? Did you install a whole system or just do a condenser swap?
    What pressure readings are you getting? What is discharge air temp from the registers?
    Jun 2013
    N. Canada
    Quote Originally Posted by ctpiper View Post
    Matt
    If you want to check charge via sight glass, elevate head pressure to 325.
    Some old units charged with this procedure.