    normal voltage range (vs. tolerable)

    on a typical, less than 3 year, trane system, what is the "normal voltage range" versus "tolerable voltage range" for a heat pump?

    at what point would the lower end become an issue for the electronic components, control board, compressors, etc?

    ie. Available Voltage Range, V. 198 - 264, 198 - 264, etc..

    reason I ask this is that I'm monitoring a couple houses where voltage drops occur randomly (data logger connected) and while these are transient and the equipment continues to run, how much of a tolerance exists on the lower end of the tolerable low voltage?

    more detail: three systems installed within 2005-2007, all in the same general neighborhood, houses are not fed by the same power station line, nor are they on the same transformer. occasionally, the power utility experiences brown-outs (as opposed to black out) and line voltage can drop severely.

  2. #2
    Join Date
    Feb 2003
    Location
    Huntsville,AL
    Posts
    4,125
    Post Likes
    ask Trane
    harvest rainwater,make SHADE,R75/50/30= roof/wall/floor, use HVAC mastic,caulk all wall seams!

  3. #3
    Join Date
    Mar 2007
    Location
    Myrtle Beach, SC
    Posts
    2,976
    Post Likes
    Typically +-10% rated voltage. Unit rated 208/230 Volts, 208 volts less 10% = 187 volts minimum. 230 volts plus 10% = 253 volts. so the range is 187 to 253 volts. At the low end you may need a start assist for the compressor.
    Remember, Air Conditioning begins with AIR.

  4. #4
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Since you are recording, ask the utility for the range that they are claiming to provide from their last monitoring point, which is usually the last station location (where the large transformers sit inside the fence, and feed the top wires on the local poles).

    Since most areas are not into the heavy power usage of hot weather, random drops can mean equipment problems that the utility would prefer to find out about NOW.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  5. #5
    Join Date
    Feb 2003
    Location
    Huntsville,AL
    Posts
    4,125
    Post Likes
    industrial used to be +10 -15

    but, sometimes I got down to exact voltage for unlatching a relay!
    and the time interval for such unlatching, then total clearing time and arc extinction time -- maybe in a few cycles= total time lapse.
    harvest rainwater,make SHADE,R75/50/30= roof/wall/floor, use HVAC mastic,caulk all wall seams!

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •