Results 1 to 11 of 11
    Jun 2013
    Northeast Wi
    Goodman gsx1330 compressor
    Im replacing the compressor next week. Along with the liquid line drier would you install a suction line drier? The valves are bad on this compressor. Both pressures are reading the same
    Oct 2010
    Only if it were a burn out and acid was present in the system.
    Chapel Hill
    I always use QwikCheck for acid test before replace compressor
    Tallahassee, FL
    Look for what killed the valves
    Jun 2013
    Northeast Wi
    What would make the valve go bad? The unit is 3yrs old. I really didnt think to much into it being a warrant replacement. Both pressure held at 220psig
    May 2011
    Western, KY
    Quote Originally Posted by 11crv View Post
    You sure it was running?
    Jun 2013
    Northeast Wi
    Positive.
    Tallahassee, FL
    Forgot to mention scrolls don't have valves
    May 2011
    Western, KY
    Positive.
    Is this a heat pump and is it a scroll compressor?
    Jun 2013
    Northeast Wi
    Not a heat pump. Yes it is a scroll.
    May 2011
    Western, KY
    The only valve you have then is a discharge check valve. If it's running but not pumping it would have to be a problem with the scroll plates not moving.
    BTW, not trying to do anything but be thorough here.
    Were all of these confirmed:
    Line voltage on compressor side of the contactor
    Did you take an amp draw reading on the wires coming off the compressor?
    Confirm capacitor?
    If yes and all was ok did you then check the windings?
    It's just not very often you get a scroll that won't pump but doesn't go out on overload, trip a breaker or have another component bad.