    That' R8 2 inch duct board
    You have got to learn from other people's mistakes! Because God knows you don't live long enough to make them all yourself !!!!!!!!

  2. #22
    Join Date
    Nov 2010
    Location
    Central Florida
    Posts
    592
    Post Likes
    Thread Starter
    I have one other new theory/question to run by you guys...

    I had speculated at the beginning of the thread maybe the 5 degree increase being seen at most ducts was due to attic infiltration in the supply plenum over the AHU. However, what is the chance that instead there may be infiltration at each individual duct where it connects to the ceiling vents? If the flex ducts were not properly fastened/sealed at time of installation, might this explain how attic air could be infiltrating? I do know that one of my neighbors' HVAC company made this exact finding and she paid to have all the ducts properly fastened.

    Thoughts?

    If I were to go dig through the blow-in insulation and inspect a few vents, what would clue me in as to whether I need to call for inspection.... should I see tape, mastic, zip-ties, something else?

  3. #23
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,847
    Post Likes
    Quote Originally Posted by SonicExplorer View Post
    I have one other new theory/question to run by you guys...

    I had speculated at the beginning of the thread maybe the 5 degree increase being seen at most ducts was due to attic infiltration in the supply plenum over the AHU. However, what is the chance that instead there may be infiltration at each individual duct where it connects to the ceiling vents? If the flex ducts were not properly fastened/sealed at time of installation, might this explain how attic air could be infiltrating? I do know that one of my neighbors' HVAC company made this exact finding and she paid to have all the ducts properly fastened.
    I said earlier that supply ducts do NOT induce infiltration into them. Supply ducts are under a positive pressure, so it is difficult for air from outside the duct to enter into it.

    That said, where the ceiling supply registers connect to the "boot" (the sheet metal box where the duct enters in), there is often a sizable gap between the ceiling drywall and the metal boot. Take the grill off and you'll see this. And when you see it, SEAL IT! Mastic tape works well for this.

    If I were to go dig through the blow-in insulation and inspect a few vents, what would clue me in as to whether I need to call for inspection.... should I see tape, mastic, zip-ties, something else?
    Hopefully you'll see duct wrap before you see duct. Beneath the wrap...it's anyone's guess from here whether it's sealed or not. Not likely is a safe bet. What you want to see is mastic on all joints, including where the boot hits the ceiling, even on the attic side. But hitting it with mastic from the interior of the house works just fine if you don't want to dig through insulation.
    Psychrometrics: the very foundation of HVAC. A comfort troubleshooter's best friend.

  4. #24
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,021
    Post Likes
    The boot to ceiling connection, if not sealed, can cause a Venturi effect that pulls in hot attic air and mixes with the cooled air as its thrown from the diffuser. http://www.alpinehomeair.com/related/Duct%20Leakage.pdf

  5. #25
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,847
    Post Likes
    Quote Originally Posted by jtrammel View Post
    The boot to ceiling connection, if not sealed, can cause a Venturi effect that pulls in hot attic air and mixes with the cooled air as its thrown from the diffuser. http://www.alpinehomeair.com/related/Duct%20Leakage.pdf
    This is true...and about the only place I would expect to see infiltration occurring along the supply duct chain. The rest of the air escaping into the attic from the supply duct actually depressurizes the house, causing infiltration to occur through the building itself elsewhere.
    Psychrometrics: the very foundation of HVAC. A comfort troubleshooter's best friend.

  6. #26
    Join Date
    Nov 2010
    Location
    Central Florida
    Posts
    592
    Post Likes
    Thread Starter
    Update:

    Today I pulled one register and the boot/box is flush to the drywall. I also put the thermometer up into the duct, well past the boot. Same result, still gaining about 5 degrees. So the boot is not the main source of infiltration. I also went over to the other neighbors' home who's house is exactly like mine, and who had her ducts re-fastened as well, and she has the same anomaly going on, gaining about 5 degrees between the AHU supply and the register of the shortest duct run.

    So....mystery remains.

  7. #27
    Join Date
    Dec 2010
    Location
    On a Peninsula in NE NC
    Posts
    1,904
    Post Likes
    Quote Originally Posted by SonicExplorer View Post
    Update:

    Today I pulled one register and the boot/box is flush to the drywall. I also put the thermometer up into the duct, well past the boot. Same result, still gaining about 5 degrees. So the boot is not the main source of infiltration. I also went over to the other neighbors' home who's house is exactly like mine, and who had her ducts re-fastened as well, and she has the same anomaly going on, gaining about 5 degrees between the AHU supply and the register of the shortest duct run.

    So....mystery remains.
    Its not a mystery. You are picking up heat from the attic. Cool the attic down. Add a attic fan.

  8. #28
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,847
    Post Likes
    Measure your temperature rise with the system running late at night. Then measure it again in the middle of the day. Post your findings here.
    Psychrometrics: the very foundation of HVAC. A comfort troubleshooter's best friend.

  9. #29
    Join Date
    Nov 2010
    Location
    Central Florida
    Posts
    592
    Post Likes
    Thread Starter
    Okay, here's the numbers. It has been a bit overcast during the days lately so the attic temps are about 10 degrees lower than normal, but at least you can get an idea....

    Night: Attic Temp = 80f, AHU = 50f, Duct (< 10ft away from AHU) = 53f (Diff of 3f)
    Day: Attic Temp = 115f, AHU = 52f, Duct (< 10ft away from AHU) = 56f (Diff of 4f)

    From past measurements, the diff increases another 1f (total of 5f) when attic temps are at true peak of about 125f+ This is where I came up with the original comment that 5f is being gained between the AHU and the nearest duct run (less than 10ft). And to recap, the part that is thoroughly perplexing is that during the day when temps are measured at the FARTHEST duct (about 50ft) the total gain is only about 2 degrees more than the shortest run, meanwhile the SHORTEST run is gaining 5 degrees being less than 10 ft from the AHU. ???? From a layman's perspective, the logical conclusion seems that something near the AHU is introducing about 5f gain into the entire system.

  10. #30
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,331
    Post Likes
    ...Very Low air flow?!

    ... Junction boxes and flex duct will ALWAYS be an issue.!

    ... A series of junction boxes is a True KILLER.!
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

  11. #31
    Join Date
    Jul 2005
    Posts
    7,834
    Post Likes
    Quote Originally Posted by SonicExplorer View Post
    Okay, here's the numbers. It has been a bit overcast during the days lately so the attic temps are about 10 degrees lower than normal, but at least you can get an idea....

    Night: Attic Temp = 80f, AHU = 50f, Duct (< 10ft away from AHU) = 53f (Diff of 3f)
    Day: Attic Temp = 115f, AHU = 52f, Duct (< 10ft away from AHU) = 56f (Diff of 4f)

    From past measurements, the diff increases another 1f (total of 5f) when attic temps are at true peak of about 125f+ This is where I came up with the original comment that 5f is being gained between the AHU and the nearest duct run (less than 10ft). And to recap, the part that is thoroughly perplexing is that during the day when temps are measured at the FARTHEST duct (about 50ft) the total gain is only about 2 degrees more than the shortest run, meanwhile the SHORTEST run is gaining 5 degrees being less than 10 ft from the AHU. ???? From a layman's perspective, the logical conclusion seems that something near the AHU is introducing about 5f gain into the entire system.
    Your blower motor adds a couple of degrees.

    Using the temp rise formula

    deltaT = kw X 3413 /(CFM X 1.08)

    Assuming something like 1 kw for the motor and 1400 CFM for airflow

    deltaT = 2.26° rise due to fan motor heat.

  12. #32
    Join Date
    Nov 2010
    Location
    Central Florida
    Posts
    592
    Post Likes
    Thread Starter
    The measurements taken at the AHU were taken directly ABOVE the AHU, so any heat generated by the fan is already largely reflected in the readings.

  13. #33
    Join Date
    Jul 2013
    Posts
    2
    Post Likes
    This is the Ask Our Pro's forum, and only Pro members that have been vetted by the AOPC may post advise, commentary, or ask questions of the OP here.

    You can find the rules for posting and qualifications here.

    Further infractions may result in loss of posting privileges.
    Last edited by beenthere; 07-30-2013 at 05:57 AM. Reason: Non Pro * member

  14. #34
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    az10101, this is the Ask Our Pro's forum, and only Pro members that have been vetted by the AOPC may post advise, commentary or ask questions of the OP here.

    You can find the rules for posting and qualifications here.

    Your post has been deleted.
    Further infractions may result in loss of posting privileges.

  15. #35
    Join Date
    Jul 2013
    Posts
    2
    Post Likes
    This is the Ask Our Pro's forum, and only Pro members that have been vetted by the AOPC may post advise, commentary, or ask questions of the OP here.

    You can find the rules for posting and qualifications here.

    Further infractions may result in loss of posting privileges.
    Last edited by beenthere; 07-30-2013 at 06:37 AM. Reason: Non Pro * member

  16. #36
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    az10101. Read the link in the post I made earlier. You are not allowed to post in other peoples threads in the AOP. Please read site rules, thank you.

  17. #37
    Join Date
    Nov 2010
    Location
    Central Florida
    Posts
    592
    Post Likes
    Thread Starter
    New finding that I need to test again tomorrow, but it seems something else additional (or related) may be going on...

    The measurements I had taken for the purpose of this whole discussion was after the system had been running during a cycle for 10+ minutes or so. However, today I tested (just by feel) the air coming out of various ducts within the first minute or so of a cycle starting. And what I found is that the air coming from the registers via ducts that run directly from the supply plenum which the AHU is connected to seem to very quickly begin blowing cool air. Not cold, but cool and certainly not warm or hot. HOWEVER, all the other ducts on the far side of the house blow hot air initially and then warm air for a good minute or two before starting to cool. Now, all those particular ducts have one thing in common, they connect to another juncture box that has a "main run" that connects to the supply plenum over the AHU. The extra length of those longer ducts is not much, not enough in my mind to possibly be making the difference I'm feeling between those that connect directly to the plenum over the AHU. To a layman like myself, this is telling me that maybe I should give a good once-over to that second juncture box? That box by the way is as high in the attic as any duct, and higher than the supply plenum box over the AHU. Is it possible the extra heat at that higher elevation may be at play as well? Do those boxes that are made out of duct board tend to be poor on keeping heat out, say worse than the R6 ducts themselves? If so, would it hurt to add some thin insulation on/around areas of that juncture box? That thing really should have probably been put on the floor of the attic. Why they left it elevated and with secondary runs coming off from above is beyond me.

  18. #38
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,847
    Post Likes
    Is that second junction box shaped like a triangle? If so, my condolences. If not, I am still sorry for your loss.

    Air in motion within a duct can thermally stratify. I may have said this earlier in the thread but it bears repeating. The section of ducts that run warmer may have nothing to do with how short or long they are, but rather what kind of air they got from the main supply plenum. If it wasn't 55 degree air (more or less) that entered the secondary run, then it's a combination of coil bypass, gain through the insulation via a hot attic, and thermally stratified air not mixing completely as it heads toward the second junction box.

    If you are eaten alive with curiosity, get a long temperature probe and start poking your ducts full of holes in various places to measure air temperature. Just patch the holes when you finish. If that sounds extreme for you to do yourself, it should. You would be better off getting a better duct design installed.
    Psychrometrics: the very foundation of HVAC. A comfort troubleshooter's best friend.

  19. #39
    Join Date
    Nov 2010
    Location
    Central Florida
    Posts
    592
    Post Likes
    Thread Starter
    Quote Originally Posted by Shophound View Post
    Is that second junction box shaped like a triangle? If so, my condolences. If not, I am still sorry for your loss.
    Yes. Triangle shaped. One big duct entering and 4 smaller ones exiting (2 each on the other two sides) And, the box is almost twice as high as it needs to be. The top of the biggest duct connects at a point not much above the center. So I could wrap the entire upper half of the box in insulation if that might help. The top of the box is less than 10" from the roof decking.

    Theoretically, I could alternatively saw off the top half and re-mastic the top back on so the extra box space is no longer there, and it would then also be further from the roof decking. That's more than I'd probably feel comfortable risking though.

    If you think the insulation idea might help please let me know. I could also put a piece on top of the main supply plenum. As long as that isn't going to create some strange vapor/condensation effect of any sorts it would be easy enough to do. Or, I could get more duct board and put another layer or two in those areas.

Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •