    What is the best method to braze 7/8 and 3/8 HVAC copper line set to brass service valve. Any help will be welcome.
    Thanks in advance
    In a machine room
    White paste flux, and 45% silver.
    In a machine room
    Welcome here by the way, you will get more answers if you post in the tech to tech chat section.
    Quote Originally Posted by Chuck View Post
    Better yet, I can just move it there...
    Moved this to tech to tech chat
    Mar 2009
    Mid-Mo
    Anytown USA
    Flux coated 45% silver rods work well.
    Jul 2000
    Northern Wisconsin
    What everyone said above +
    The best method is the one that when done not only meets the manufacturer's specifications, it also doesn't damage the service valves.
    Don't forget the nitrogen.
    Jul 2002
    SE Texas
    Stay-Silv 15 and white flux.
    With your chrome heart shining in the sun, long may you run.
    Cincinnati, Oh
    It's not brass.
    but, for the goodman condenser your installing, dynaflow.
    "Just get it done son."
    Dad adjusted
    Jul 2013
    Thanks for the tips. Seems like White paste flux, and 45% silver is the "method of choice"
    Yes I'll be using nitrogen.
    Oct 2010
    5-15% silphos is all you need for connecting the copper line set to the service valve stubs on a condenser if that's what you're doing.
    In a machine room
    Quote Originally Posted by jtrammel View Post
    True
    Worry is a really gross misuse of one's imagination. -- PHM
    Nov 2008
    DFW,TX
    True
    x3
    45% and flux is over kill( that is used for true solid brass/stainless) and 15 stay-silv/silfoss etc etc is all you need NO FLUX but pull valve caps, shroeder cores, a good wet rag over valves plus a good oxy/acet rig with good hot heat go fast and true then pour water over repair area immediately after your done.. check for leaks with Nitro, 250 for 22 and 400 plus for 410, and your golden..