    trane heat pump

    looked at a trane heat pump yesterday. model geha, water source,serial # wooa01162. compressor wouldn't start, tripping on overload. replaced compressor today. unit started fine, but suction went down to 0 psi in a few seconds. high side went to 230-240. tryed 4 or 5 times, always went 0 right away.

    thinking txv must have failed. unit is hanging in attic with horrible access, not sure what else could cause it to suck down so quickly other than txv? i caould only run a few seconds at a time becuase it was pumping down so quickly.

  2. #2
    Join Date
    Aug 2004
    Location
    Chapel Hill
    Posts
    117
    i have this alike experience. In my case, i have a clogged up TXV. It was like dirt trap inside the TXV.

  3. #3
    Join Date
    Mar 2013
    Location
    swan valley idaho
    Posts
    728
    ok- when you replaced, what did you solder distributor to txv with?

  4. #4
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,356
    15%

  5. #5
    Join Date
    Mar 2013
    Location
    swan valley idaho
    Posts
    728
    ok-trane said just to use soft solder on that joint. it looked different is why i ask.

  6. #6
    Join Date
    Mar 2013
    Location
    swan valley idaho
    Posts
    728
    anybody ever used regular soft solder? the distributor to valve connection is very tight /close, trane is saying to use regular lead free soft solder- just doesn't sound right.

  7. #7
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,356
    Soft solder is for plumbing. Is the distributor brass?

  8. #8
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,356
    I use 45% on unlike metals such as copper to brass, copper to stainless, etc. I use 15% on copper to copper.

  9. #9
    Join Date
    Oct 2004
    Location
    Central WA
    Posts
    1,537
    It's a heat pump - shift into heating and see if your pressures come around. A clogged up or failed txv will still usually bypass/check in reverse.

  10. #10
    Join Date
    Mar 2013
    Location
    swan valley idaho
    Posts
    728
    it's in a hotel ceiling and guest is back, so i had to leave for now. i also use 15% ,and thought soft solder didn't sound right, their tech support said to use it so valve dosen't get to hot? i've always used wet rags around valve.

    cjp- i did not try in heat mode. if power head failed it will pull right down to 0 in heat also right? if i do have normal pressure in heat, then i probably had crap in valve that got blown out in heat? it pumps down so quick-like 3 seconds, i cant think of anything else but txv. it will be a royal PITA to change this valve

  11. #11
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,356
    I have some water source heat pumps I take care of. When I have to replace txv or rev valve, I use a genie duct lift to lower the unit from the ceiling. Repair unit on lift then push it back up in ceiling. It's not too bad of a job like that.

  12. #12
    Join Date
    Mar 2013
    Location
    swan valley idaho
    Posts
    728
    I found I can get just power head through rsd, trane said whole valve only. I'm thinking power head is dead and would fix it. Any similar experiences and should I try this or just suck it up and change the whole valve.

  13. #13
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    4,054
    It's a bi-directional Txv which meters both ways. I agree that most likely the power head is bad

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event