    Loop Sealing - Anyone?

    I have a 3 ton Geo system I installed 2 years ago for a customer which has worked great until now, the lake loop piping is leaking and losing pressure. The leak must be very small since it takes 6 to 8 weeks to leak down from 45 psi. Have any of you guys used a sealant product in a leaking loop and if it worked can you provide the name and source of the sealant? I have asked my suppliers and no one offers such a product. My only other option would be to float the loop to check for leaks. Thanks for any help.

  2. #2
    Join Date
    Feb 2009
    Location
    Portland OR
    Posts
    2,577
    Post Likes
    I would want to find out where and why the loop is leaking if its not to tough to bring it up, because you want to make sure the mistake is not made again if its your mistake or if its the manufacturers mistake what to look for or lastly if its an environmental factor so you know for future use. We tell customers a loop should never leak and we install close to 50 systems per year without one leaking yet(knock on wood) All but two of ours are in the ground, one is on a floating home and one we are installing(4 systems actually one home) is on a pond.
    Check out my YouTube channel - http://www.youtube.com/user/skyheating1 We have customer testimonials, product reviews and more!
    Like us on FACEBOOK if you like our advice here!

  3. #3
    Join Date
    Aug 2009
    Location
    Maine
    Posts
    7,985
    Post Likes
    Didn't think the EPA allowed a loop in a lake, pond or the ocean.

    Quote Originally Posted by SkyHeating View Post
    I would want to find out where and why the loop is leaking if its not to tough to bring it up, because you want to make sure the mistake is not made again if its your mistake or if its the manufacturers mistake what to look for or lastly if its an environmental factor so you know for future use. We tell customers a loop should never leak and we install close to 50 systems per year without one leaking yet(knock on wood) All but two of ours are in the ground, one is on a floating home and one we are installing(4 systems actually one home) is on a pond.

  4. #4
    Join Date
    Jan 2012
    Location
    Roosevelt, Utah
    Posts
    32
    Post Likes
    I don't think there's any problem with a closed loop system placed in a body of water.

    To the OP, I would reccomend that you go ahead with floating the loop and fixing the leak. I know of one installer that used a leak-stop solution (no idea what brand), but it didn't work at all. In the end, he would have been better off finding and fixing the problem.

    Good luck!

  5. #5
    Join Date
    Aug 2009
    Location
    Maine
    Posts
    7,985
    Post Likes
    Local restaurant wanted to use a closed loop in Casco bay. EPA said no way. I guess they were worried about a leak and also heating the water in the summer.
    A good (if there is one) truck radiator stop leak ? Probably a good exercise in futility. Mine is exercised
    daily.

    TE=ClarkBP;16204301]I don't think there's any problem with a closed loop system placed in a body of water.

    To the OP, I would reccomend that you go ahead with floating the loop and fixing the leak. I know of one installer that used a leak-stop solution (no idea what brand), but it didn't work at all. In the end, he would have been better off finding and fixing the problem.

    Good luck![/QUOTE]

  6. #6
    Join Date
    Oct 2011
    Location
    Gladstone, Oregon (Portland)
    Posts
    414
    Post Likes
    Did you go cheap at the beginning? Leaks are rare. You had an amateur installing your loops.

  7. #7
    Join Date
    Mar 2012
    Location
    West Berlin, NJ
    Posts
    59
    Post Likes
    EPA did not approve the bay loopfield because it is just that....A bay.
    You must own the waterway your going to use for the loops. In NJ we are not allowed to have closed loops in the bay either, but lakes,creeks,rivers ponds are fine if you own them or have run off to them for open loops.
    Dan Callahan
    www.CallahanWellDrilling.com
    Get "well educated" with us!

  8. #8
    Join Date
    Jun 2013
    Location
    NORTHERN
    Posts
    1,178
    Post Likes
    Quote Originally Posted by virginiatech View Post
    ... leaking and losing pressure....from 45 psi. ... used a sealant ....to float the loop to check for leaks. Thanks for any help.
    in one school a bars stop leak liquid
    [not cotton-fibers, etc] worked well, permanently and one bottle per well-loop; but others can advise for you:
    however,
    the Hydro-Temp, AR, system
    has very low pressure drop loop hx not coaxial, generally, (under 4ft tdh in glycol, 2.7gpm/actual compressor label-ton) with I guess more open cross section, etc.) and none of the HX loses performance nor pluggs. Check your OEM, miscible-oil in body of water? May be just presurize and find leak/ as SKY...

    Any stop leak with the fibers can quickly get in to the volutes of the impellers of the circulators, or y-strainers that the bars passes right through.

    SKY is best above advice, if you can do the likes of adding air pressure
    Also?
    45 psi? A reservoir in joists off T is only 2 psi and plenty of NPSH over pump inlets at 4ft TDH + (5+ better).

    We have systematically since 1983 "left" the pressurized loop world, and never voided a warranty BECAUSE 2 psig is pressure:

    The GFos tech said he'd like 6ft but minm 4.1/2 on a ph call about T'd in reservoirs in overhead joists above the impeller of the pump , used commonly since the 70's.
    AND
    one-size over-sized - T body of the fitting , receiving the EW from the Earth-Coupled ECL, gle, loop-field, to get solution incoming under 4 ft/sec, generally is better (but size of header line does work to purge air).
    have used 1.1/2" to 2"T's but 90% 1.1/4" for most 1.1/4" header lines.

    This T is 90-deg on its side, EW dead-heading into the horizontal base leg, then splitting to the (a) shut off, to a simple 5 gal carboy (to 15 tons) [ 2.1/2gal 3 ton, 4 pipes or smaller than 1500 ft loops, ] overhead-above in oists or nearly so.
    -
    some times there before that shut off between it and the T is a t'd boiler drain for future quick customer add-in as AIR EFFERVESCES CONSTANTLY for a few months out of solutions...
    Solutions of ground loops are gassing 99% of the time and AUTO-PURGE T-designs need no "splitters" other than the T's

    We have NEVER had to add additives to 16-18% methanol (but always if under 24% glycol per dowfrost's recommendations).
    The vented reservoir with ~ 4 gal in a 5 gal tank DOES NOT LOSE methanol, as a layer of , bacteria or debris forms on the fluid top in the plastic container.

    Many schools, 500+ ton (largest surgical center in GT, US, by 2004) and 30,000 homes of just one OEM most-all have had this and by design, some several years before some OEM's claimed warranties void if no pressure... since the late '70 's - still a fine air-purging today.

    The pumps are under the other side of the T-head turned on its side ALWAYS over 4ft TDH for better NPSH and yields better pump performance than standin QT type flow centers. (seen since 1996)

    This maintains all flowing well such that even 18 feet ABOVE this T and reservoir, if headers and lines hit that ~ 2.3 to 2.4 feet per second/air-moving out of piping methanol antifrozen, then and IF NO LEAKS at all , it can be in the basement above the pumps, with higher headers, but pump inlets underneath the T.

    (that depends on flow and drag and possible cavitation, but an un-pressurized reservoir top will not flood under 18 feet rest of design.)

    Systems can run "rather-OK" BELOW Reynolds numbers in lines, headers built for flushing, once the air is gone (99.%)

    Just 3% en-trained air can cause some systems to require 2 pumps for some 4-tons sized systems to better-perform, mechanically but then less efficiently...
    where as 1 pump works well
    to most of today's 4.1/2 and 5 sized-tons to 5 pipe systems (averaging over 20-tons per hp) with a simple T-in reservoir design for most homes, I believe..
    Process cooling: NO COMPRESSORS Earth-Coupled since 1996
    ... however, much still needs to be hybridized energy transfer.

    CLOSED LOOP 2015 listed EER's
    even 49+ now; and "blended from low to high variable speeds" for 32deg.F ~ E-Star

    Perhaps you need a 32F Chiller/HW-Heat: buy a GEO-T Heat Pump (GHP with Heat-Recovery)
    http://www.energystar.gov/index.cfm?...mal_heat_pumps

    http://www.hydro-temp.com/products.html and Bosch/Carrier and AquasystemsInc.com

  9. #9
    Join Date
    Jan 2013
    Location
    Milton,Pa
    Posts
    20
    Post Likes
    I have heard of some using a Stop-Leak for pools and spas but i wouldn't reccomend it. Best to find the leak and fix it.

  10. #10
    Join Date
    Jun 2013
    Location
    NORTHERN
    Posts
    1,178
    Post Likes
    Quote Originally Posted by Geo medic View Post
    I have heard of...it.
    agreed bests; but even a couple teaspoons of table pepper have found and stopped small leaks in pressurized systems according to a 25 year vet in GT and now dominating in horizontal boring.

    Reservoirs T'd in over the flow center just leak slower, if leaking, at having less than pressurized loop problems with leaks that can not be found. - Make sure flow PD is well enough for the NPSH at the pump inlet, though.
    Process cooling: NO COMPRESSORS Earth-Coupled since 1996
    ... however, much still needs to be hybridized energy transfer.

    CLOSED LOOP 2015 listed EER's
    even 49+ now; and "blended from low to high variable speeds" for 32deg.F ~ E-Star

    Perhaps you need a 32F Chiller/HW-Heat: buy a GEO-T Heat Pump (GHP with Heat-Recovery)
    http://www.energystar.gov/index.cfm?...mal_heat_pumps

    http://www.hydro-temp.com/products.html and Bosch/Carrier and AquasystemsInc.com

  11. #11
    Join Date
    May 2008
    Location
    Missouri
    Posts
    4,464
    Post Likes
    We've switched some older "slow leaking" loop systems (put in by others) to non-pressurized pump/tank systems (made by B&D manufacturing). They work fine.

  12. #12
    Join Date
    Jun 2013
    Location
    NORTHERN
    Posts
    1,178
    Post Likes
    Quote Originally Posted by wahoo View Post
    We've switched some ... B&D manufacturing). They work fine.
    What ChrisJ in the Hydro-Temp q's is referencing is the reservoir over the pumps, which allows for a higher NetPositiveSuctionHead, and smaller pump horsepower per ton.
    Not so big a deal but does allow for 1 pump to what is called size 5.5 to size 6 units having 56k to 64k btu compressors inside of the systems.

    Grundfos tech in the early 90's with theups 26 - 99 then, said a good 5 ft of fluid pressure, on a T-in , above the pump was great for the performance NPSH assist.
    Those pressureless sure are great for air removal as pressurized systems contain disolved air that also interears with pump performance, as heat exchanger and pump OEM's point out in various articles and literature.

    you may want to check the cavitation affecting the pumps bodies with those low level reservoir set ups. Reservoirs overhead are hitting 21 years, same pumps.

    FlowCenterProducts com has an add-on to improve the low tank flow centers performance, and get a few more btu's available.
    Process cooling: NO COMPRESSORS Earth-Coupled since 1996
    ... however, much still needs to be hybridized energy transfer.

    CLOSED LOOP 2015 listed EER's
    even 49+ now; and "blended from low to high variable speeds" for 32deg.F ~ E-Star

    Perhaps you need a 32F Chiller/HW-Heat: buy a GEO-T Heat Pump (GHP with Heat-Recovery)
    http://www.energystar.gov/index.cfm?...mal_heat_pumps

    http://www.hydro-temp.com/products.html and Bosch/Carrier and AquasystemsInc.com

  13. #13
    Join Date
    Dec 2008
    Location
    South Jordan Utah
    Posts
    158
    Post Likes
    we have had good luck with Loop Conditioner from Geothermal Supply for fixing leaks
    Dewayne Dean

    www.palacegeothermal.com

    See my live system data here:

    We Heat and Cool with Dirt