    The gas condenses to a liquid...pressure collapses and stays that way. The condenser fills with liquid. There is no transfer of heat in the evaporator. Talking single/dual cap tubes & refrigeration circuits.
    Two pages to discuss this, I'm out.
  2. #28
    Jul 2013
    Quote Originally Posted by Frostmonkey74 View Post
    The same result as when a cap tube plugs.... While the compressor is pumping out the refrigerant in the low side of the system, the head pressure will climb " momentarily" how ever if you were to leave it to run in a vacuum, as you would see with any system with a plugged capillary tube, you wild find the high side pressure would drop as well.. Next time you pump down a system watch your gauges, next time you're working on a ref system set up for pump down watch how it works ... Same principle ... If the compressor isn't moving any refrigerant it cannot develop head pressure!
    Stand corrected. I guess I was thinking more of a major restriction with a unit with a high pressure switch.
  3. #29
    Jun 2012
    Wisconsin
    if you wanna know if your cap tube is plugged look for frost..... The refrigerant will release its pressure and the temp of the refrig will drop inside of the cap tube. Think a mini cap tube inside of a cap tube
  4. #30
    Oct 2009
    Raleigh, NC
    Quote Originally Posted by Bseliger View Post
    Greater than 90% of the time cap tubes become restricted (today) along their entire length with buildup on the walls of the tube. You won't find any frost.
  5. #31
    Next time you pump down a system,watch the high side,does it go up or down?
  6. #32
    Just saw frostmonkes post, I am with him,less heat taken in less to reject! But a high discharge temp,with a restriction, due to high superheat.
  7. #33
    Jun 2013
    NORTHERN
    refer or rfg
    Quote Originally Posted by bwd111 View Post
    ... if refer .. so pressure would ...
    DROP as seen on a beach once in Clearwater; -true! i did not inhale, but they were no i did not spellcheck.
    rfg
  8. #34
    Jun 2013
    NORTHERN
    Quote Originally Posted by coolperfect View Post
    Next time you pump down ...
    if pumping into the cdsr, it changes - higher only a little, enough to fill the cdsr.
    eh?
  9. #35
    Jul 2013
    Stupid question. If you're pumping a system down, you close the liquid port and pull in through the suction. Then close your suction. Your head is obviously going to go down because you're reading the pressure in the line set and you're pulling it in. Right? I know I was wrong earlier. I don't get what you're trying to say now.
  10. #36
    Quote Originally Posted by Tommyz23 View Post
    High Side would be on the DSV ,no closing of suction,So in effect the king valve is a restriction!
  11. #37
    Jul 2011
    Nanaimo,BC, Canada!
    When you pump a system down by front seating the king vale on the receiver the gauge port on the king valve is still on the high side if the system. ( refrigeration condensing unit not AC/heat pump unit) so there for is still sensing high side pressure..
  12. #38
    Jun 2013
    NORTHERN
    What FM said!
  13. #39
    Yakima, WA
    So, I heard somewhere that refrigerant has a PT relationship when liquid and vapor is present. So whether you have 1 lb or 30 lbs of R22 in a bottle the pressure at a given temp will be the same, and whether you have a little or a lot of liquid in a condenser coil the pressure at a given temp will be the same as well...
    Also, I had an instructor years ago always saying "heat is pressure." Technically kind of a misnomer, yes, but it takes you back to basics and has always stuck with me. If your metering device is restricted you are starving the evaporator, and thus not picking up heat. If you are not absorbing heat your pressures will be low.