    In my experience it primarily appears in the form of entropy.
    What's the prize?
    PHM
    Quote Originally Posted by bwd111 View Post
    Think of it this way as vapor is compressed work is done on the vapor increasing both the pressure and energy of the vapor. In other words its going to make everyone think here if you can answer it the energy added to the molecules of the vapor appears in what form. Latent heat,sensible,specific or superheat. Winner gets a prize
    PHM
  2. #93
    Jul 2013
    Harrisburg, PA
    Sensible heat. Not latent because it's not changing state, not specific because that's just a measurement compared to water, and superheat is just a measurement, not an actual heat unit.
  3. #94
    Jul 2013
    Harrisburg, PA
    Quote Originally Posted by Poodle Head Mikey View Post
    What's the prize?
    PHM
    I'll go with that.
  4. #95
    Oct 2009
    Raleigh, NC
    There still is a pressure and temp with subcooling and superheat. I can razor the pressure and have high superheat or lower the pressure and have lower superheat. For every temp there is a pressure behind it
    Not in blend situations. For refrigerant blends with large glides, there can be a range of temps for a specific pressure.
  5. #96
    Jul 2009
    new york
    Quote Originally Posted by MicahWes View Post
    A simple question has gone to 8 pages.
  6. #97
    Well; it would be about like this:
    If the cap tube gets restricted, AND you are the first one on the scene following that event, you will find that three things are low and three things are high.
    Low:
    1. The suction pressure
    2. The refrigerating effect
    3. The head pressure
    High:
    1. Suction superheat
    2. Compressor temperature
    3. Conditioned space temperature
    On the other hand, if you are the second, third, or fifth person to get there you will not find many more low things but you may well find some more high things:
    Additional high things:
    1. Head pressure
    2. Subcooling
    3. The anger level of the owner
    Why do you want to know these things? Do you have a specific project presently under the knife?
    PHM
    Since one flows the other if cap tube is plugged would pressures be the same lower than normal on both sides or would you see something more like higher pressure on high side and lower than normal on lowside
    PHM
  7. #98
    Maine
    I know and I droped out after 5 pages:-)
  8. #99
    In a boiler room
    Low:
    High:
    1. Head pressure
    2. Subcooling
    PHM
    Best answer so far, this agrees with my experience. If the owner doesn't tell me that someone else worked on it and I find high SC and high head pressure I go ask him "has someone been working on this?" Owner; "umm, why do you ask? my brother(or friend or dad or neighbor or dog) is handy with stuff and said it was just low on freon"
  9. #100
    Southeastern Pa
    Quote Originally Posted by Chuck View Post
    That's a good example of how this is rarely, if ever, a perfect world, one where our theoretical ideas about the systems are borne out in fact.
    Sometimes, you can only see something that is vaguely the same shape as a condenser coil....
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
  10. #101
    Jun 2013
    NORTHERN
    2 points, and neither found in your poodle !
    Then how do you explain superheat and subcooling?
    PHM
    Process cooling: NO COMPRESSORS Earth-Coupled since 1996
    ... however, much still needs to be hybridized energy transfer.
    CLOSED LOOP 2015 listed EER's
    even 49+ now; and "blended from low to high variable speeds" for 32deg.F ~ E-Star
    Perhaps you need a 32F Chiller/HW-Heat: buy a GEO-T Heat Pump (GHP with Heat-Recovery)
    http://www.energystar.gov/index.cfm?...mal_heat_pumps
    http://www.hydro-temp.com/products.html and Bosch/Carrier and AquasystemsInc.com
  11. #102
    Jun 2013
    NORTHERN
    Best answer so far,"
    xactly mon palli !
    and too , yes superheat aint a heat unit unless yz get a media x temp to get a thing of heat, or two.
    3)
    just blew the cap tube of the poppa in law adding stop leak "oh I was careful,,...." (!)
    450 psi CO2 i use to blast cdrs-coils with
    ---(but I am careful to not bend fins after the first three or four are re-straightened...).
  12. #103
    Oct 2009
    I fixed a beer cooler recently new compressor and cap tube everything looks normal except a 5psi suction pressure, using 134 a refrigerant, thermostat cut off system @ 36 f
  13. #104
    Jul 2009
    new york
    Quote Originally Posted by tech#1001 View Post
    Sounds great