    Quote Originally Posted by walden.raccoon View Post
    You're using A different gas? O,,o

    My fault..it's an r22 replacement
    Yes its an r22 replacement and I made sure I ran a good vacuum also

  2. #15
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,039
    You got power problems id bet. What's the amp draw on common. Also common and run together and start only?

  3. #16
    Join Date
    Jul 2013
    Posts
    63
    Have you checked amp draw? If the other ones posts blew out, it sounds like it may have been running hot as well. Filter?

  4. #17
    Join Date
    May 2013
    Location
    California
    Posts
    108
    Filters are clean. I will hop into the attic today and check how clean the coil is. But assuming all that is good and the amp draw is too high, what could possibly be causing it?

  5. #18
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,338
    Does this compressor have the preformed terminal connector (as found on many copeland scrolls) or is it the type that you wire each lead individually?

    If it is the preformed connector, look at your female spades closely. Sometimes they get loose and cause a bad terminal connection.

  6. #19
    Join Date
    May 2013
    Location
    California
    Posts
    108
    Quote Originally Posted by socotech View Post
    Does this compressor have the preformed terminal connector (as found on many copeland scrolls) or is it the type that you wire each lead individually?

    If it is the preformed connector, look at your female spades closely. Sometimes they get loose and cause a bad terminal connection.
    Yes its a copeland that you just basically plug in. I'll check to make sure its not loose also. Thank you for the suggestion!

  7. #20
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,338
    Quote Originally Posted by IsaiahV View Post
    The old one still has the correct MFD

    Yes liquid line drier was replaced, and yes this unit has a txv.

    Thank you for all the replies!
    Are you sure the compressor is even pumping for two minutes? You said MFD on capacitor is correct, but did you verify with a meter?

  8. #21
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,338
    Quote Originally Posted by IsaiahV View Post
    Yes its a copeland that you just basically plug in. I'll check to make sure its not loose also. Thank you for the suggestion!
    I bet that's your problem.

  9. #22
    Join Date
    May 2013
    Location
    California
    Posts
    108
    Quote Originally Posted by socotech View Post
    Are you sure the compressor is even pumping for two minutes? You said MFD on capacitor is correct, but did you verify with a meter?
    I can only get refrigerant in when the compressor kicks on, so I'm guessing it is pumping when the compressor kicks on. If the capacitor is bad, wouldn't my compressor not kick on? Or do you think the capacitor could be affecting my amps even though it has the right mfd?

  10. #23
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,338
    I would at least check mfd of capacitor for +-5% of rated value. I do think a weak capacitor can cause higher amp draw.

  11. #24
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,039
    I usually seat that peckerhead with a mallet.

  12. #25
    Join Date
    May 2013
    Location
    California
    Posts
    108
    Quote Originally Posted by socotech View Post
    I would at least check mfd of capacitor for +-5% of rated value. I do think a weak capacitor can cause higher amp draw.
    Heres a pic of the capacitor, it appears to be within range.
    Name:  Photo Jul 07, 2 28 14 PM.jpg
Views: 229
Size:  49.8 KB

  13. #26
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,338
    Yea. That's ok.

Page 2 of 6 FirstFirst 123456 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event