Results 1 to 13 of 17
    N.J.
    expansion tank pressure
    We have a school with a chilled water system. The system is 300 tons of d.x. and quite large in reference to the piping layout and length of run.We are gong to replace the verticle expansion tank due to a ruptured bladder. My question is ,what is the formula for figuring out what to charge the new tank to . I'm told it will come pre charged to 12 psig,but I dont think that will be enough pressure to satisfy our verticle lift . Many thanks in advance.
    Adjust the air charge to the system fill pressure.
    Illinois
    Quote Originally Posted by richper
    I dont think that will be enough pressure to satisfy our verticle lift.
    Ok, how tall is your system? You need to know that before you can figure your fill or tank pressure.
    Short-loop syndrome? This is a completely different problem, but you probably already knew that..
    "If I had my life to live over again, I'd be a KA." - Albert Einstein
    It's later than you think.
    The Gray Northwest
    How can you have a chill water system with 300 tons DX?
    You need to know your system volume, delta T of your loop, how many feet of pump head you have and so on.
    Check this out: http://www.taco-hvac.com/en/library.html
    Quote Originally Posted by maggio View Post
    This is the correct answer. Make sure this is done with no pressure on the water side.
    Take empty tank.
    Fill air side equal to you system fill pressure.
    Install tank.
    The Gray Northwest
    Quote Originally Posted by RLJ79 View Post
    Take empty tank.
    Install tank.
    System static fill pressure, plus system head, plus 3 psig.
    Where are you getting this info? I am looking at an install manual right this minute.
    Hampton Roads, Virginia
    As long as the expansion tank is piped very close to the system fill pressure regulating valve, then precharge to system fill pressure before connecting the water side. If expansion remote from fill, then other factors need to taken into consideration.
    "There is plenty of room at the top because very few people care to travel beyond the average route. And so most of us seem satisfied to remain within the confines of mediocrity." -- Benjamin Nnamdi Azikiwe, first president of Nigeria
    "It's not the customer's job to know what they want." -- Steve Jobs
    The Gray Northwest
    Just finished a new tank installation. You have to know system volume so you can determine the tanks acceptance volume if it's a new tank. All tanks come with a 12 psi pre-charge which works for most single story applications. If you're pumping to a rooftop or in a multi strory building you also have to take into account the head pressure on the system. What is the highest point of your system? If it's 30 ft the formula would be: 30 x 0.5 + 3 psi residual = 18 psi air charge. The residual is added to compensate for the head pressure so you can eliminate the air in the system. If you undercharge the tank, you'll reduce the acceptance capacity.
    Yes thats how to calculate the required fill pressure, the system volume is indeed needed to correctly size the expansion tank.
    Quote Originally Posted by big johnson View Post
    System volume is one of the factors needed to size an expansion tank. Also, the system fill pressure should be already determined by you building height...correct? Otherwise the water pressure would be insufficient to make it to the top of the building.
    Illinois
    Take empty tank.
    Install tank.
    So how do you know the fill pressure is right?