Page 4 of 4 FirstFirst 1234
Results 40 to 52 of 52
Thread: TXV issue?
  1. #40
    Jun 2013
    It seemed to me that the openings in the blower compartment door for return air were way to small and few . Like I said too when the door was off my subcool was right on target at 9. With door on it shot up to 11.9
  2. #41
    Aug 2008
    San Clemente, CA
    When you get the model numbers we will know the a/c system size. Some of these furnaces are rated for 2 ton's and some for 3. If your installing a 3.5 or 4 ton a blower kit will need to be installed to replace the existing blower. Here is some info on this.
    Manufacturer documents attached.
  3. #42
    Jun 2013
    Coleman mod 7956856
    Ser 048880382
  4. #43
    Jun 2013
    It used to have a 3 ton rheem r-22 system but compressor burnt out maybe for the same reasons that are causing these problems
  5. #44
    Jun 2013
    I had the customer remove the blower door and it never froze up for a week. I modified the blower door with two 16" square filter grilles and installed pleated filters. The next morning it froze up. House was 70 and they had stat set at 68. I told customer to repair the gaping holes in the flex duct in the crawl. (He doesn't want to pay me to do it) I also advised a new blower motor with three speeds so it can be set to move more cfm's. I am wondering if the furnace and duct system is too small for the new 3 ton system. The model numbers to all equipment are as follows: furnace: Coleman 7956856; coil: Mortex 96R36YOP, ser M0130130146 ; Condenser: Rheem RANLO37JAZ. I also find it strange that it usually freezes when they try to draw the temp down below 70. I'm not sure why that's necessary anyway. Frosting starts right at the outlet of the txv.
  6. #45
    2-16X16 filter grilles are a bit small for 3 tons.
  7. #46
    Feb 2012
    central Florida
    It is not a good idea to put the system to go below 70-72. I have seen this cause systems to freeze.
  8. #47
    Dec 2008
    Buffalo NY
    Quote Originally Posted by techbill11 View Post
    I run mine at 68 with no issues.
    Sent from my iPad using Tapatalk HD
    Join http://scopeny.org/ Shooter’s Committee on Political Education
    The world is full of sheep,try not to join the flock.
    Support the Skilled Trades, Don't DIY
  9. #48
    Quote Originally Posted by Tommyz23 View Post
    A unit will not ice up when it's over charged.
    You just made me remember something from my childhood! Westhinghouse had a package unit that used a txv valve, that used SC to work with a big accumulater, the bulb on the LL,many a guy kept adding gas only to freeze more!
  10. #49
    Quote Originally Posted by qwerty hvac View Post
    You can do that, when you have good air flow.
  11. #50
    Dec 2008
    Buffalo NY
    I didn't read the the whole thread. Doh
  12. #51
    LOL, yeah I sometimes skip too many post and don't realize I missed the important parts.
  13. #52
    Jan 2006
    McQueeney, Texas
    Was there a part where the coil was looked at for being clean? Use a strong flashlight and see if you can see through it?
    I may have missed parts of the conversations here.
    The metal door stamped face types are tightly done- I use the needle nose and bend them open some.