    Confused Carrier Infinity problem

    Has anyone seen a fault of VC startup volt. Outside was giving me a code of VC/VH fault. While checking out it just started and went faults were gone. still in history. Any ideas.

  2. #2
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,836
    I think it's because you didn't have power to the outdoor unit before the indoor.

  3. #3
    Join Date
    Feb 2007
    Location
    texas
    Posts
    9
    8 faults and never reset power

  4. #4
    Join Date
    Mar 2003
    Posts
    1,215
    The outdoor board is probably flashing a 6 code which means a voltage out of range-either too high or low. Usually there is an issue with the kick-start relay which is particular for those 2 stage units. If the comp. will operate just replace the kick start relay and cap. that come together. HC95DA401 for a 5 ton unit or HC95da700 for a 4 ton.

  5. #5
    Join Date
    Feb 2007
    Location
    texas
    Posts
    9
    It was flashing 9 but that is what I was thinking. Thanks