Has anyone seen a fault of VC startup volt. Outside was giving me a code of VC/VH fault. While checking out it just started and went faults were gone. still in history. Any ideas.
-
04-03-2007, 10:12 PM #2
Banned
- Join Date
- Aug 2002
- Location
- Office and warehouse in both Crystal River & New Port Richey ,FL
- Posts
- 18,836
I think it's because you didn't have power to the outdoor unit before the indoor.
-
04-03-2007, 10:14 PM #3
Regular Guest
- Join Date
- Feb 2007
- Location
- texas
- Posts
- 9
8 faults and never reset power
-
04-04-2007, 11:51 AM #4
Professional Member*
- Join Date
- Mar 2003
- Posts
- 1,215
The outdoor board is probably flashing a 6 code which means a voltage out of range-either too high or low. Usually there is an issue with the kick-start relay which is particular for those 2 stage units. If the comp. will operate just replace the kick start relay and cap. that come together. HC95DA401 for a 5 ton unit or HC95da700 for a 4 ton.
-
04-04-2007, 10:06 PM #5
Regular Guest
- Join Date
- Feb 2007
- Location
- texas
- Posts
- 9
It was flashing 9 but that is what I was thinking. Thanks