Thread: cfm's in a ton

  1. #1
    Join Date
    Apr 2007
    Posts
    1

    cfm's in a ton

    How many cfm's in a 1-ton unit, a 15-ton unit and a 20-ton unit?

  2. #2
    Join Date
    Jan 2002
    Location
    Fort Worth\Dallas, Texas
    Posts
    1,699
    Nominal CFM would be 400 per ton. This will vary on the application.
    Go Rangers!

  3. #3
    Join Date
    Nov 2006
    Location
    South-Western, ON, CAN
    Posts
    64
    and I think about 450cfm for heat pumps, if you're talking BTU cooling 12,000 BTUH is one ton of cooling.

  4. #4
    Join Date
    Mar 2007
    Location
    NJ
    Posts
    23
    Quote Originally Posted by lwarren View Post
    Nominal CFM would be 400 per ton. This will vary on the application.
    unless of course were talking liebert my boy....

  5. #5
    Join Date
    Mar 2004
    Location
    SE Michigan
    Posts
    17,898
    Quote Originally Posted by jern View Post
    and I think about 450cfm for heat pumps, if you're talking BTU cooling 12,000 BTUH is one ton of cooling.
    That would be 350 for heat pumps.
    " Kill a Commie for Mommy! "

    - Colonel David Hackworth (1930-2005), Korean War Vet

  6. #6
    Join Date
    Jun 2002
    Location
    Dacula, GA
    Posts
    12,551
    Quote Originally Posted by coolwhip View Post
    That would be 350 for heat pumps.
    I allways shoot for 400 a ton but I learned that you got to have a minimum of 300 and a max of 400 a ton.
    "I could have ended the war in a month. I could have made North Vietnam look like a mud puddle."
    "I have little interest in streamlining government or in making it more efficient, for I mean to reduce its size. I do not undertake to promote welfare, for I propose to extend freedom. My aim is not to pass laws, but to repeal them. It is not to inaugurate new programs, but to cancel old ones that do violence to the Constitution."
    Barry Goldwater

  7. #7
    Join Date
    Mar 2004
    Location
    SE Michigan
    Posts
    17,898
    Never put in a HP, maybe Im thinking of the heat side being cooler so you dont want quite as much cfm...Im tired.
    " Kill a Commie for Mommy! "

    - Colonel David Hackworth (1930-2005), Korean War Vet

  8. #8
    Join Date
    Mar 2006
    Posts
    266
    400 cfm per ton is just a rule of thumb. You should check each manufacturer for specific info.
    Anything worth doing, is worth doing right......the first time!!!

  9. #9
    Join Date
    Mar 2007
    Posts
    22
    Quote Originally Posted by stltechfrmtx View Post
    400 cfm per ton is just a rule of thumb.
    "Ton" refers to a BTU rating not really CFM. 12,000 = Ton

  10. #10
    Join Date
    Mar 2006
    Posts
    266
    Quote Originally Posted by RLJ79 View Post
    "Ton" refers to a BTU rating not really CFM. 12,000 = Ton
    But when most reference cfms in terms of a unit, the "rule of thumb" is for every 12000 btus there should be 400 cfm.

    its just easier to say cfm per ton
    Anything worth doing, is worth doing right......the first time!!!

  11. #11
    Join Date
    Mar 2007
    Posts
    22
    # Heat pumps and air conditioners are generally sized in tons. Typical sizes for single family residences are between two and five tons. Each ton equals 12,000 Btuh. It is important to note that actual capacity is not constant and will change based on outdoor or indoor temperatures. The published capacity rating of air conditioners and heat pumps is based on performance at the ARI standard temperature levels of 95 F outside, 80 F inside.
    www.hannabery.com/hvacwords_2.shtml

    # unit of refrigeration - equal to 12,000 Btu's/hour
    www.aaronprocess.com/glossary.asp

    # A unit of measurement for cooling capacity. One ton = 12,000 BTU's per hour
    www.helmsheating.com/HVAC%20GLOSSARY.htm

    definitions from Internets.

  12. #12
    Join Date
    Jan 2002
    Location
    Fort Worth\Dallas, Texas
    Posts
    1,699
    Quote Originally Posted by lwarren View Post
    Nominal CFM would be 400 per ton. This will vary on the application.
    I have some 60 ton watersource heatpumps running 170 cfm per ton. Of course they are 100% OA units and they don't work worth a crap.
    Go Rangers!

  13. #13
    Join Date
    Mar 2007
    Location
    NJ
    Posts
    23
    actually fellas you should design your cfm per ton around the calculated load design... example... if i had a home with alot of living biological plants ie trees open water etc.. one would design for higer for latent.. if i had alot of glass but very little lantent loads i would design for higher ensible loads etc. etc. etc. you just need to know what your cooling before you can say cfm per ton. ive had loads come in at 550 per ton and ive had some at 350 per ton.. same tonnage just different cfm per ton.. so the lesson is design first then cfm to accomadate..

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event