    VAV system with cfm flow charge out

    The clients wanted to do charge out rate to the tenant for air condition used.

    The problem arises when One unit AHU is supplying to 4 different Tenants per floor.
    I have been told to use the VAV air flow to do CFM totalizer eventually to do charge out rate.

    However, I don't agree with the concept using VAV to do charge out rate since the VAV does not act independent as fcu or vrv system.
    I know there is kw/hour, btu/hour but i never heard of cfm/hour.

    Would appreciate anyone can share some thoughts on this issue or can direct me to the explanation website/page since i am in controls system.

    Thank you.

  2. #2
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,320
    The VAV boxes proportionally take air from the air handler that was cooled either by DX or chilled water. The only way to measure the amount of air delivered to a given zone is via the flow rings in each VAV box (converting FPM to CFM).

    i think your greater challenge is determining what an equivalent rate for CFM/hour might be as compared to a chilled water meter (gallons consumed). The air handler blower requires energy, along with the VFD, and whatever means employed to chill the AHU coil. And you're dividing that among four tenants, each of whom may have more than one VAV box per tenant space. CFM totalization seems your only route...figuring out a rate to charge...maybe your client just wants you to set up the CFM/hour totalization on the front end and let them worry about what to charge. If so, I would do as they ask and let them worry about the money angle.
    • Electricity makes refrigeration happen.
    • Refrigeration makes the HVAC psychrometric process happen.
    • HVAC pyschrometrics is what makes indoor human comfort happen...IF the ducts AND the building envelope cooperate.


    A building is NOT beautiful unless it is also comfortable.

  3. #3
    Join Date
    Feb 2006
    Location
    Float'N Vally, MS
    Posts
    1,824
    If I understand you correctly, they want to charge the tennant $ for CFM delivered.
    This can be calculated (CFM turned into BTU's or KW x $), but I can see some serious problems down the road, if you have VAV problems (and you will).

    We have a controls system where the building areas, Chillers, AHU etc. have power meters on them. The client is charged for the %of energy used according to his floor space. Because of lease contracts this is in the implecation process only, but in time this will be the standard way of billing.
    Life is too short, Behappy!
    TFMM

  4. #4
    Join Date
    Aug 2009
    Location
    Jurupa Valley, CA
    Posts
    1,777
    If they are trying to proportionally split the costs among tenants that utilize the same AHU, then the VAV flow is the only way to split it up. You still ahve to have some metering on the AHU to meter how much energy IT is using, then you take that total energy use, and split it by the same proportions of the total CF delivered to each zone over the time period.

  5. #5
    Join Date
    Jan 2007
    Location
    Stongsville Oh
    Posts
    895
    If I were the tenant I would ask that my min cfm is set to zero. Do these vav's have any form of reheat? Just kidding about the zero cfm min. I think a supply airflow station should be utilized to check the accuracy of vav cfms. Most systems now have trending capabilities so trending of each vav in groups per tenant would be how I approach it. Trending of suplly air cfm would indicate totals to check tenant totals against.
    ckartson
    I didn't write the book I just read it!