Results 1 to 13 of 21
    Jan 2013
    SMAN 4 ISSUE STRIKES AGAIN.
    Well, after applying more closing torque to my high side valve than is considered reasonable for a quality manifold I got the refrigerant leak-by to stop..
    Only problem now is the clamps don't stay calibrated.
    Three jobs the readings didn't seem right and three times they were off by up to three degrees. And I had re calibrated them all three times to 32*f.
    I used a 557 and and calibrated SMAN 3 to make my comparisons and they verified the SMAN 4 was reading wrong.
    So much for my participation in the wireless revolution.
    So you are blaming the wireless now?
    I thought you had "calibration" issues in the past with the none wireless unit.
    Oct 2008
    Fullerton
    Hvac5646 has had this problem before but he's the only one I've had come back with this specific problem and in testing I've never seen this. His issue is that the SMAN3 and 4 thermocouples will fluctuate throughout the day. Can some of the SMAN3/4 regular users who regularly calibrate their thermocouples share their experiences with calibrating the thermocouples?
    In a machine room
    Could it be some sort of interferenc? There are some YouTube videos of different electronics or static affecting thermocouple readings.
    Worry is a really gross misuse of one's imagination. -- PHM
    Seen error from clamp design and could easily be what this is about especially of he is comparing to better clamps or measurement methods.
    Oct 2010
    I've never calibrated my fp clamp probe that use with my hs36 and its within 1* of my other thermistors and thermocouple probes/clamps.
    Apr 2012
    Cleveland
    Mine seem to stay pretty accurate on the sman3. My high side has been consistently 5* off for the last 2 days and my low side is about 1* off. I will re calibrate them tomorrow on my day off.
    The issue that I've been having with mine for the past couple weeks is both sensors fluctuating temperatures then coming back to normal very quickly. It seems like its losing its connection with the manifold because sometimes it goes to oL also.
    In a machine room
    Quote Originally Posted by Hvac216 View Post
    One of our guys with sman3 has that intermittent ol too.
    Jan 2013
    lol...no not blaming the wireless function...just saying that since I can't keep them in calibration I cant rely on them to give me accurate SC and SH so I will have to side line my SMAN 4 until I can resolve the issue. That takes away the WB function of the wireless on the SMAN .
    Apr 2012
    Cleveland
    Quote Originally Posted by Chuck View Post
    That really sucks. I love the gauges and the features, just don't like the thermocouples.
    Jan 2013
    Quote Originally Posted by RussellHarju View Post
    You haven't tested mine yet Russ, how can you say 'I am the only one"? There was a similar situation with certain instruments syncing up with the HG3 and then you found out there was a glitch in the software.
    I posted in a thread my SDP2 would not sync with HG 3 and your response was "It won't sink up?"with no other follow up. Like you disbelieved it. Than you issued a firmware patch for the HG3.
    No offense, just stating what happened.
    So, saying "5646 is the only one having this issue" is premature.
    Jan 2013
    I don't recall saying I had the same issue with my SMAN 3. But than, you guys were kind enough to send me three exchange by over night air, so maybe I was referring to one of those.
    I really don't remember.
    Jul 2010
    nebraska
    Russ, the problems with my SMAN 3 temp clamps comes from two areas. Most of the time it's a nearly broken wire in the K end. Not too big of a deal, cut the end off and put a new one on. The second issue the plastic in the female half is weak. Had one crack the top off so the little retention spring wouldn't make good contact with the male prongs because it wasn't compressed enough.
    Once the connection problems were solved the erratic readings went away.