    venting of public restrooms

    I am bidding a remodel job on a convenience store with two public restrooms.

    mens- 1 urinal and 1 commode, 10' x 12'.
    womens- 2 commodes, 10' x 12'.

    They want to use one roof mounted exhaust fan for both restrooms. the fan will switch on with the lights with a occupancy sensor.

    I can't find my code book at this moment. Thanks BSC

  2. #2
    Join Date
    Aug 2005
    Location
    Navarre Florida
    Posts
    131
    I believe it is 2 CFM per square foot of floor area

  3. #3
    Join Date
    Jan 2006
    Posts
    208
    I was thinking the code was 70 CFM per commode & 50 CFM per urinal, but I am not for sure. BSC

  4. #4
    du mech eng is offline Professional Member-BM-bad email
    Join Date
    Nov 2003
    Location
    Philadelphia
    Posts
    80
    international mechanical code says 75 cfm per fixture (whether it be toilet or urinal).