Results 14 to 26 of 30
    Aug 2012
    Norman Ok
    Yeah there great to have got one on the key chain and one in the truck got mine from the grundfos rep
    Jul 2012
    CT
    Thanks puff-noeyebrows that would be great.
    Caledonia WI
    Pm me with your address and I will send you one Monday.
    Aug 2012
    Norman Ok
Size:  300.7 KBName:  20130701_134832.jpg
    Aug 2001
    Pavilion, NY
    I want one!
    Jun 2013
    Austin, TX
    One trick I have used to check for AC magnetic fields is to take a Hall current probe, hold it open, and wave it around the motor or whatever. You can't get a quantitative measurement out of it but you can check for current in the windings without even removing the cover. (Particularly well shielded motors and transformers might not give any measurable magnetic field, but you probably won't see any in HVAC.)
    Jan 2011
    Ottawa, Canada
    Viessman gave them away when we had training for their boilers... Cept th writing is in German!
    Sent from my SGH-I747M using Tapatalk 4 Beta
    Dec 2010
    ND
    These can be found at vjkindicator.com for approx. $5.00 ea. Just ordered a couple after the boss lost a similar one. I hope this helps.
    in a house, Appomattox, Va.
    You can unscrew the cap off end of some circulators and see the end of shaft spinning
    Col 3:23
    Aug 2009
    Ottawa ON
    I have had to open the end cap. The grundfos tester only shows the presence of a rotating mag field in the windings. Not if the stator is actually moving.
    The one I had was seized but the tester showed me it was working
    Central NJ Area
    Use your amp probe to see if the circ pump is operating. Check the rated motors amp draw on the plate. High amp draw the motor or impeller is most likely seized. No amp draw with voltage applied most likely open winding. Low amp draw would indicate that the impeller is not spinning and just the motor is. Just use your electrical knowledge to diagnose the pump. You could also check delta t across the boiler to see if its moving the water at the right GPM, only if the boiler is fired properly according to your combustion analyzers reading.
    That little tool is pretty cool though. I like to have one!
  12. Likes N2fords liked this post
  13. #25
    Jan 2014
    Idaho
    Quote Originally Posted by Zionone View Post
    These work awesome for checking if a solinoid is energized. You can feel the magnetic field much better than with a small screw driver.
  14. #26
    Central NJ Area
    They make a magnet to move on reversing valves, or testing them. They come in really hand when working on heAt pumps and to check their is no delta t across the inlet and out let of the reversing valve.
    I use a screw driver sometimes to check to see if the solenoid is energized and working. You can feel the pull on the scredriver tip.