    I apologize, haven't read full thread. Sorry if these are old ideas. Have you made sure everything is sized correctly for the box/ wall thickness? Is there a stat/ solenoid? What about a door switch? Suction line heat exchanger? Power head an SZ? As long as you have superheat, the comp should be ok
    Last edited by Rwilson404; 07-11-2013 at 12:32 AM. Reason: Wasn't done

  2. #80
    Join Date
    Sep 2002
    Posts
    21,435
    Post Likes
    Thread Starter
    Well; after my first glance I started off with the late night hip-shoot "diagnosis" that the TXV was defective / not feeding. So I checked the compressor HP (1/2 HP) and then chose a 1/4 ton valve because that is about what flows enough BTU's at a -10 F. suction. When replacing it I found that the "bad" TXV was both the exact same valve AND was clearly very new. <g>

    I called the box maker; Norlake and got the original specs: 1/2 HP K body Copeland compressor - they did not know which one they had used.

    The almost-new compressor was then found to be rated from -40 to 0 F. That was the second WTF moment.

    The ZP valve would only feed to a 50 lb. suction. This took very little refrigerant in the warm evaporator coil. The resulting refrigeration effect was very small. So the box stayed too warm to ever let the suction pressure reduce enough to allow the TXV to feed more refrigerant. A catch-22 loop.

    1. I have never in my life seen a Norlake box which would do what it was rated to do.
    2. A half horse compressor is what should be on a single door reach-in freezer - not on a six by six walk-in.
    3. A 3/4 HP -10 condensing unit was less expensive than the correct 1/2 HP K body - and plus; the old condenser was filthy with gummed on fryer grease that I had no interest in touching.

    So I installed the 3/4 HP Copeland tin can condensing unit the customer needed.

    This worked better but subsequently it was discovered that on an earlier visit by one of the others in my peer group the system had been improved by eliminating the fan delay, the defrost termination, and all the wiring associated with them. And they also set up the box for four 45 minute, time-terminated defrosts per day. I found to my painful surprise that this both increases the evaporator to a skin-blistering heat level And also serves to heat the box substantially when the fans come on as soon as the defrost times out.

    I don't have a whole life to continually devote to this project so at this point I have the larger condensing unit holding the box temperature at about 9 F. using four 15 minute minute time-only defrosts per day.

    As soon as I get some free early morning time I am going to rewire the system to re-include fan delay and evap coil temperature termination of defrost.

    That will not be today however. <g>

    BTW: This is a Norlake box. Norlake is a company which apparently dismisses such frivolities as sufficient wall thickness, solenoid valves, a door switch, and a suction line heat exchanger.

    PHM
    ------


    Quote Originally Posted by Rwilson404 View Post
    I apologize, haven't read full thread. Sorry if these are old ideas. Have you made sure everything is sized correctly for the box/ wall thickness? Is there a stat/ solenoid? What about a door switch? Suction line heat exchanger? Power head an SZ? As long as you have superheat, the comp should be ok
    PHM
    --------
    The conventional view serves to protect us from the painful job of thinking.

  3. #81
    Join Date
    Jun 2013
    Location
    NORTHERN
    Posts
    1,178
    Post Likes
    Quote Originally Posted by Poodle Head Mikey View Post
    "What's...mean?--
    Is it possible to improve with a simple TimeDELAY on the defrost start timer/ set-up, and adjust so that for another 3 or 4 minutes, the defroster does not kick in (D on mk); and if not yet installing last posted changes to do....? (you know, if still getting defrosted-enough to drop more temp)
    -
    M: ya Probably have seen the gas-mask required -- or hold breath and run-from vapor:
    Blaster
    of solvent that really works nicely on old gummy-bear cdsr fin clogged w/ kitchen greazzzzz (!)
    (I saw you did not wanna...)

    the What's above:
    Were are the temps at 5 am? before the door opens? Just 9 ?

    -OF 9 subways - just have not any Norlake control issues yet nor problematics...
    but they run cheaper on getting them to switch their uty electrics and gas billings at CCM's options energy team choice improvements...(!) and I get the portion as an adv fee as a commission every time they turn on the power/heat! (enrolled 87 / 18 commercially !

    Did find fitting on the compressor needed tightening, and recharged new rfg.

    Pan under evap that was not draining was just tapped-bent differently than OEM to then drain...

    Still curious as to what your end is, let us know, pls.

    I'll use less abrv-French next time.
    Process cooling: NO COMPRESSORS Earth-Coupled since 1996
    ... however, much still needs to be hybridized energy transfer.

    CLOSED LOOP 2015 listed EER's
    even 49+ now; and "blended from low to high variable speeds" for 32deg.F ~ E-Star

    Perhaps you need a 32F Chiller/HW-Heat: buy a GEO-T Heat Pump (GHP with Heat-Recovery)
    http://www.energystar.gov/index.cfm?...mal_heat_pumps

    http://www.hydro-temp.com/products.html and Bosch/Carrier and AquasystemsInc.com

  4. #82
    Join Date
    Aug 2009
    Location
    Maine
    Posts
    7,999
    Post Likes
    But they are cheap. If I remember the coolers used to be ok in the 70's. But that was then and this is now.


    Quote Originally Posted by Poodle Head Mikey View Post
    Well; after my first glance I started off with the late night hip-shoot "diagnosis" that the TXV was defective / not feeding. So I checked the compressor HP (1/2 HP) and then chose a 1/4 ton valve because that is about what flows enough BTU's at a -10 F. suction. When replacing it I found that the "bad" TXV was both the exact same valve AND was clearly very new. <g>

    I called the box maker; Norlake and got the original specs: 1/2 HP K body Copeland compressor - they did not know which one they had used.

    The almost-new compressor was then found to be rated from -40 to 0 F. That was the second WTF moment.

    The ZP valve would only feed to a 50 lb. suction. This took very little refrigerant in the warm evaporator coil. The resulting refrigeration effect was very small. So the box stayed too warm to ever let the suction pressure reduce enough to allow the TXV to feed more refrigerant. A catch-22 loop.

    1. I have never in my life seen a Norlake box which would do what it was rated to do.
    2. A half horse compressor is what should be on a single door reach-in freezer - not on a six by six walk-in.
    3. A 3/4 HP -10 condensing unit was less expensive than the correct 1/2 HP K body - and plus; the old condenser was filthy with gummed on fryer grease that I had no interest in touching.

    So I installed the 3/4 HP Copeland tin can condensing unit the customer needed.

    This worked better but subsequently it was discovered that on an earlier visit by one of the others in my peer group the system had been improved by eliminating the fan delay, the defrost termination, and all the wiring associated with them. And they also set up the box for four 45 minute, time-terminated defrosts per day. I found to my painful surprise that this both increases the evaporator to a skin-blistering heat level And also serves to heat the box substantially when the fans come on as soon as the defrost times out.

    I don't have a whole life to continually devote to this project so at this point I have the larger condensing unit holding the box temperature at about 9 F. using four 15 minute minute time-only defrosts per day.

    As soon as I get some free early morning time I am going to rewire the system to re-include fan delay and evap coil temperature termination of defrost.

    That will not be today however. <g>

    BTW: This is a Norlake box. Norlake is a company which apparently dismisses such frivolities as sufficient wall thickness, solenoid valves, a door switch, and a suction line heat exchanger.

    PHM
    ------

  5. #83
    Join Date
    Dec 2008
    Location
    NW Iowa
    Posts
    249
    Post Likes
    PHM- what was the end result? I've been waiting for over a year to find out.