Thread: Indoor coil freezing up

  1. #1
    Join Date
    Feb 2010
    Location
    Seattle, Wa
    Posts
    6
    Post Likes

    Indoor coil freezing up

    split system - r22 with fixed meetering device carrier condenser and goodman gas furnace 100k btu. This is an old unit in one of the our fire stations. pre inspection, after unit was thawed showed clean filter - we change them out quarterly, clean indoor and outdoor coils, airflow good on both coils, voltage and amps good. Low side was 40 psi and high 190 but due to quickly freezing up I din't have a chance to check the superheat and subcooling. I recovered the refrigerant, nitro pressure tested it with no leaks. Although they looked clean, I cleaned both coils, orfice for the fixed meetering device (screen look debris free) and replaced the filter drier. Pressure tested again all good. evuacated the system and charged the system. Had a hard time getting all 7lbs back in the system. Suct pressure was good 65-70 psi, super heat 12 subcooling in the 40s Discharge was 290 and raising quick. vsp was 45deg and lst was 110 deg. Any ideas would be much appreciated.

  2. #2
    Join Date
    Aug 2001
    Location
    Mechanicsville, Virginia
    Posts
    2,042
    Post Likes
    Quote Originally Posted by osci View Post
    split system - r22 with fixed meetering device carrier condenser and goodman gas furnace 100k btu. This is an old unit in one of the our fire stations. pre inspection, after unit was thawed showed clean filter - we change them out quarterly, clean indoor and outdoor coils, airflow good on both coils, voltage and amps good. Low side was 40 psi and high 190 but due to quickly freezing up I din't have a chance to check the superheat and subcooling. I recovered the refrigerant, nitro pressure tested it with no leaks. Although they looked clean, I cleaned both coils, orfice for the fixed meetering device (screen look debris free) and replaced the filter drier. Pressure tested again all good. evuacated the system and charged the system. Had a hard time getting all 7lbs back in the system. Suct pressure was good 65-70 psi, super heat 12 subcooling in the 40s Discharge was 290 and raising quick. vsp was 45deg and lst was 110 deg. Any ideas would be much appreciated.

    Your stated pressures, superheat and subcooling values don't jive with your stated saturation temperatures.

    Recover refrigerant until you get some stability with your pressures and temps, then repost your measurements. Include ambient, indoor dry and wet bulb as well.

  3. #3
    Join Date
    Feb 2010
    Location
    Seattle, Wa
    Posts
    6
    Post Likes
    Thread Starter
    will do thanks

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •