Results 1 to 8 of 8
    Aug 2012
    Monticello, IL
    Display of VAV CFM erratic and now 0
    We have Delta's DVC-V304A controllers on our VAV boxes. On one of the units the CFM is erratic and is not reading correctly (typically reads lower than actual.). After speaking with Delta and them checking out the programming they said the issue was the controller. We replaced the controller and still have the same issue. Anyone have any ideas? Could some of the holes in the air sensor be clogged?
    Feb 2007
    Helena, Montana
    I'm not familiar with that specific model, but have seen tubes get holes in them over time. I would check all of the tubing. I would think the sensor would get clogged if filters are changed regularly, but stranger things have happened.
    Don't worry zombies are looking for brains, you're safe...
    Aug 2012
    Monticello, IL
    Thank you will check that. There doesn't seem to be an easy way to get into the sensor to check that section of the tubing.
    Apr 2011
    Chicagoland Area
    It's usually the tubing, not the sensor. Most of the time people will install a "T" and put a rubber plug over the "T" port, these tend to dry rot and crack. If your lines are good, then check the sensor itself by connecting main air to each (the hi and low), this will hopefully blow out any debris that may have clogged it.
    Aug 2012
    Monticello, IL
    Thanks for the input. I began paying closer attention to rest of the VAV boxes in that building and noticed several that are erratic. About half are on one AHU and the other half on another. The building is only 10 years old.
    Also, it is not a pneumatic system. Could we use canned air to try and blow out the sensors or, if not, bring in a small compressor?
    Apr 2011
    Chicagoland Area
    Absolutely, you can use whatever air you want. You wouldn't want to use too high of an air pressure (20-25 psi should be sufficient).
    May 2009
    in the present
    If you don't have enough straight duct up stream, you can have too much turbulence at the sensor and see this type of issue.
    Aug 2012
    Monticello, IL
    Quote Originally Posted by kirkH View Post
    Thanks. I have been suspicious of that. This box is about 2' after a 90.