    trace refrigerant
    Since R-22 has become so expensive, I don't want to use it as a trace gas for chiller leak check. In the past I would use R-22 and nitro, What are you guys using now?
    ottawa canada
    Why use trace refrigerant ... Whats wrong with nitrogen and soap or my personal favorite........ Snoop . I only use trace refrigerant as a last resort ...what about 134a ??
    The Hot South
    134A.
    If its a low pressure chiller, there will be some residual refrigerant in the chiller after you recover the gas. Just put nitrogen in and your good to go.
    Apr 2013
    Portugal
    In Europe its forbidden use any refrigerant that cause Global warming as a tracer. If we can´tt find the leak with Nitrogen and soap, we use a corant mixed in the oil.
    22 still works. 134a is ok, but starts to condense if you want to go real high (just below the relief valve pressure setting). we have discussed using 410a but we have yet to use it.
    Dec 2006
    Somewhere in Canada
    Very interesting, What is a "corlant" mixture?
    Dec 2006
    Somewhere in Canada
    I goofed ... please What is a "corant" mixture?
    Jan 2011
    Quote Originally Posted by Ph-D View Post
    I believe he meant "colorant" (dye) mixed with the oil.
    Dec 2006
    Somewhere in Canada
    Thank you KnewYork, I believe you are correct. Thank You.
    Apr 2013
    Portugal
    Quote Originally Posted by KnewYork View Post