    Does higher temperature setting actually save money?

    I have a generic technical question about commercial DDC HVAC and energy savings: Can raising the summer temperature settings on a DDC system actually INCREASE operating costs? In other words, if the discharge air temp is constant at 55 degrees, do you actually need to add more reheat at the VAV boxes and thus burn more energy to keep a higher office temp? Or does the system simply run less for shorter cycle times, and it really does save money to raise the thermostat? (I am a facilities manager at a large company trying to save money by raising thermostats a few degrees. Unfortunately, I'm a civil and not mechanical engineer, so I can't say intelligently whether we'll save money or not. We have many different building types and HVAC systems, so my question is not specific to any particular setup - just asking in broad terms).

  2. #2
    Join Date
    Jun 2013
    Posts
    3
    Post Likes
    Thread Starter
    It's been a couple of days with no replies -- maybe I'm in the wrong forum? If anyone knows a better place for me to find an answer to my question, please redirect me! Thanks

  3. #3
    Join Date
    Aug 2009
    Location
    Griffin, Georgia
    Posts
    655
    Post Likes
    If you have constant discharge air at 55° then yes it will increase your energy cost to raise the thermostat if you are conditioning the air with reheat. It really boils down to what type of system you have. I would think you would do better with some way to stop the constant 55° air than try and reheat it. If you're running a steady supply air of 55° I can see q large amount of money wasted to cool areas that don't need that much constant cooling.

    Sent from my DROID RAZR using Tapatalk 2

  4. #4
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    4,042
    Post Likes
    jbcrane, could you please explain what is meant by "55&#176"? I presume "55" refers to 55 degree supply air temperature, but I'm kinda lost on the rest of it. I'm thinking "#176" refers to something about moisture content of that air (pounds mass?), but would like to be better informed. Thanks.

  5. #5
    Join Date
    Jun 2006
    Location
    New Jersey
    Posts
    4,456
    Post Likes
    &#176 is the html ascii code for °. Don't think html works in the threads.

  6. #6
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    4,042
    Post Likes
    Thanks Ascj. I've seen that a couple of times since yesterday. So, "html ascii code" is some kinda computer speak? Ignorance is not only bliss, it is sometimes confusing.

  7. #7
    Join Date
    Jun 2004
    Location
    Eugene, Oregon
    Posts
    1,015
    Post Likes
    In broad terms, yes, you will save energy by raising set points in the cooling mode.
    If you have Variable Air Volume (VAV) terminal units (TUs) you shouldn't need to reheat during the summer if the VAVs are sized and set up properly. VAV terminal units vary the airflow in cooling to maintain space temperature. If the room gets too cold the air flow will reduce down to a minimum airflow CFM. If the temperature continues to drop the TU will switch to heat and the reheat will come on. But if the TUs are not oversized you shouldn't switch over to heat during the cooling season. If it's warm enough outside the heating water system should be disabled anyways and you wouldn't be using reheat.
    If you have constant volume then yes, the air will need to be reheated if the supply air is too cold.
    There are many ways to save energy in a DDC controlled system. Raising set points in the spaces, reseting AHU discharge set points based on outside air temperatures, reseting AHU fan speeds based on demand,...etc. I would recommend you hire a consultant to audit your system and help you identify ways to save energy. With DDC controls you have a lot of control over your system and you could potentially save a lot of energy.
    "The bitterness of poor quality remains long after the sweetness of low price is forgotten". --Benjamin Franklin
    "Don't argue with an idiot, they will drag you down to their level and beat you with experience". --Mark Twain
    http://www.campbellmechanical.com

  8. #8
    Join Date
    Jun 2013
    Posts
    3
    Post Likes
    Thread Starter
    Thanks air1 and jbcrane - this is helpful feedback!

  9. #9
    Join Date
    Oct 2011
    Location
    NJ
    Posts
    149
    Post Likes
    If you do not have energy recovery units and use a large amount of outdoor air due to occupancy and it is not used for makeup for processes or other forms of exhaust and is merely relieved, then CO2 sensors can be placed through the building and used with the DDC controls to reduce incoming air to the minimum needed. Reducing incoming air can reduce load at the unit level and is a major way to reduce energy use that is just wasted going once through the unit and out.

    Adding CO2 sensors is a relatively cheap way to save a lot of energy.

  10. #10
    Join Date
    Sep 2006
    Location
    Anchorage Alaska
    Posts
    641
    Post Likes
    This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.

    You can find the rules for posting and qualifications here.

    Additional infractions may result in loss of posting privileges.
    Last edited by jpsmith1cm; 08-08-2013 at 06:14 AM.

  11. #11
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    simux

    This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.

    You can find the rules for posting and qualifications here.

    Additional infractions may result in loss of posting privileges.



Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Tags for this Thread

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •