Thread: Walk-in freezer high head pressure

  1. #1
    Join Date
    Jan 2011
    Posts
    200
    Post Likes

    Walk-in freezer high head pressure

    I have a r-404 unit remote, condensing unit on roof running at 350 on high side with about 134 sat temperature and on the low I have 4 deg sat temperature
    with the flip cover off and the outside roof temp near 100 deg, box is at 20 deg. I blew out all the dirt out of the condenser, and there was plenty, the high side does not sit still, it will fluctuate from 330-390, kicks off at 400, when it starts up, the high side immediately goes up for 5-10 seconds and nearly pops at 400 before coming down
    when I put the top down, the head pressure raises to 400 and kicks off, and has been cycling on that, thought possibly overcharged so I let some gas out till few bubbles in glass, now I am thinking moisture or noncondensables in system but my suction seems normal. I left cover part way off to keep pressure from rising, air only blows out back of cover and fan seems to want to push it out sideways so the air stays in the condensing unit longer, has been like this for several years though, anybody got anything.

  2. #2
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    Your going to have to clean that coil better then blowing it out. Get some Nubrite coil cleaner and a pressure washer to clean it good. Also is the fan on a cycling switch ?

  3. #3
    Join Date
    Mar 2007
    Location
    Madison, Wisconsin
    Posts
    2,749
    Post Likes
    First cool the CU down once with water, then try pumping down the compressor. Could be a bad discharge valve. If that is not it, it could be an uneven mix of 404, or non condensables. Recover and charge with fresh juice.
    I r the king of the world!...or at least I get to stand on the roof and look down on the rest of yall

  4. #4
    Join Date
    Jan 2011
    Posts
    200
    Post Likes
    Thread Starter
    Quote Originally Posted by Wheelbaron View Post
    First cool the CU down once with water, then try pumping down the compressor. Could be a bad discharge valve. If that is not it, it could be an uneven mix of 404, or non condensables. Recover and charge with fresh juice.
    freezer now down to 8 deg with cover the way it is, and it is raining here though, if I had a bad discharge valve, wouldn't I have higher suction pressure, and the pressure wouldn't drop on suction right because it does drop

  5. #5
    Join Date
    Jan 2011
    Posts
    200
    Post Likes
    Thread Starter
    Quote Originally Posted by VTP99 View Post
    Your going to have to clean that coil better then blowing it out. Get some Nubrite coil cleaner and a pressure washer to clean it good. Also is the fan on a cycling switch ?
    no unit has head master, no cycling switch I believe but would have to recheck that, headmaster seems to work fine, checked line going into control and it was not hot so condenser should be in play

  6. #6
    Join Date
    Mar 2013
    Location
    swan valley idaho
    Posts
    1,277
    Post Likes
    you have a few choices for very high head pressure- overcharge, air in system,dirty coil, lack of airflow.

    i would wiegh out charge, and pull a good vaccuum, then recharge to correct level. Also wash the coil very well, and use a good coil cleaner. If fan is running correctly, and you do those two things, you have pretty well addressed all common causes

  7. #7
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,573
    Post Likes
    Quote Originally Posted by VTP99 View Post
    Your going to have to clean that coil better then blowing it out. Get some Nubrite coil cleaner and a pressure washer to clean it good.
    Start here. If you have to, pull the fan and blow it out again from the inside, then wash I have also pulled the louvers off the covers and replaced with chicken wire to make sure ALL the air is being discharged from the unit. Once this is in order, you can then make the proper diagnosis if needed.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  8. #8
    Join Date
    Jul 2010
    Location
    So-Cal
    Posts
    647
    Post Likes
    Sounds to me like you need to clean that condenser real good before you do anything else!

  9. #9
    Join Date
    Mar 2013
    Posts
    44
    Post Likes
    This is an odd one but my head keeps circling back to non condensables as well. Like you're periodically freezing up the valve orfice or drier, enough to kick that head pressure way up. But you would see some fluctuation in suction pressure too, unless lineset is obscenely long. And even then. It's not your discharge valve if you can pump it down with no issues.

    Sight glass telling you anything moisture wise? And if you pump it down at the receiver and not the solenoid, can the receiver hold everything without tripping high head? And what's you're txv and distributor doing? Frosting at all? Drier colder on one side during a cycle? Compressor smoking hot or still touchable without getting 3rd degree burns? No EPR or CPR on the suction line right? (Would be a detail I'd hope you'd include =p) and what type of compressor? Recip?


    Edit# some how overlooked the post you mentioned it has a head master. <_< take an actual temp reading across those lines from inlet of HM to inlet of receiver. Be SURE that is not dumping hot gas into the receiver. Some times its not obvious by quick touch of each line. And if it going into condenser. Braze a saddle right after condenser coil, Ignore receiver service valve, and take a sub cooling measurement. Should tell you how well your condenser is dispelling heat or if you're overcharged. Assuming the headmaster is even working correctly. You have to be held up somewhere if your charge is good. Condensers get plugged from time to time as well. If you clip the headmaster and watch your head sky rocket into oblivion, then your coil is garbage.

  10. #10
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,573
    Post Likes
    The HPS is also set a little low @400psi
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  11. #11
    Join Date
    Sep 2005
    Posts
    58,704
    Post Likes
    Clean first...
    Airflow second...
    Then troubleshoot.

    Problem is... if the first two are not right... fixing the third or fourth or fifth (etc) will not fix the unit...
    GA-HVAC-Tech

    Your comfort, Your way, Everyday!

    GA's basic rules of home heating and AC upgrades:
    *Installation is more important than the brand of equipment
    *The duct system keeps the house comfortable; the equipment only heats and cools (and dehumidifies)
    *The value of comfort, over the long term; leave economic choices behind!
    Choose your contractor wisely!

  12. #12
    Join Date
    Mar 2013
    Posts
    44
    Post Likes
    And yes all my previous ramble is under the assumption the coil is ACTUALLY well cleaned and you have straight air flow through. Which I'd hope is the case. ::face palm::

  13. #13
    Join Date
    Mar 2007
    Location
    Madison, Wisconsin
    Posts
    2,749
    Post Likes
    Check your amp draw, a bad discharge valve will still show good suction pressures, but the comp will over heat, and the head press will be high and amp draw will be high. And there will be an over all loss of capacity.
    I r the king of the world!...or at least I get to stand on the roof and look down on the rest of yall

  14. #14
    Join Date
    May 2007
    Location
    maryland, baltimore
    Posts
    136
    Post Likes
    Go with the dumb s#$$@ first, turn off the power drag a hose to the unit and wash the crud out of the coil. I was talking a tech through a the same problem not long ago. He removed the charge, recharged with new 404a, adjusted the txv to who knows where, talked to tech support and they instructed him to replace the head master and txv. Box was at 10 when he started customer wanted -10, 10 hours later box was at 40. He hasn't done much refrigeration and we were really busy, had I known he was close by would stopped over to check on him. Coil looked clean on outside, but fan blades were filthy. Another company had just finished cleaning the coils on the entire strip. You couldn't see any light through the coil and when he sprayed it with nubrite the dirt started rolling out of it. We topped off the charge and it was fine. When you ask for help, the person on the other end assumes that you have exhausted the simple things first.

  15. #15
    Join Date
    Aug 2009
    Location
    Maine
    Posts
    8,146
    Post Likes
    Would a simple thing include checking the dryer? Has any one changed the fan blade? Is the suction line sized right?

  16. #16
    Join Date
    Jan 2004
    Posts
    69
    Post Likes
    Quote Originally Posted by lytning View Post
    Would a simple thing include checking the dryer? Has any one changed the fan blade? Is the suction line sized right?
    Lota techs don't think to see if the fan blade is turning in the right direction little thinghs missed wind up being your headache

  17. #17
    Join Date
    Jul 2002
    Location
    SE Texas
    Posts
    615
    Post Likes
    Quote Originally Posted by zuke19 View Post
    I left cover part way off to keep pressure from rising, air only blows out back of cover and fan seems to want to push it out sideways so the air stays in the condensing unit longer, has been like this for several years though, anybody got anything.
    I'm a little confused by this statement. Is air being pulled through the condenser coil and blown through and across the compressor or the other way around?
    With your chrome heart shining in the sun, long may you run.

  18. #18
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    Quote Originally Posted by SandShark View Post
    I'm a little confused by his statement. Is air being pulled through the condenser coil and blown through and across the compressor or the other way around?
    I am visualizing a cover for a outdoor unit,solid sides and open at the front and back.
    OP says " air only blows out back" so all that sounds right. Now the part I don't understand is "fan seems to want to push it out sideways" is there no shroud ?

  19. #19
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,573
    Post Likes
    Quote Originally Posted by VTP99 View Post
    "fan seems to want to push it out sideways"
    I missed that the first time. When you have a plugged condenser coil on an A/C unit, when you run your hand over the fan discharge, which way does it push the air? Up? or out the sides.....
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  20. #20
    Join Date
    Mar 2013
    Posts
    44
    Post Likes
    Out the sides around the parameter of the blade. If its clean you will feel it blow straight through the coil and straight onto the compressor. Assuming its directing behind where the fan motor is mounted like on most walkin condensing units.


    If air is blowing out the sides of the fan blade. Coil is clogged.

    Had one yesterday at a bakery full of flower and other powders. Literally baked a cake inside the coil 0. No air flow through and burnt up the compressor. Good times.

+ Reply to Thread
Page 1 of 3 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •