    I installed a condenser fan motor that was running at 1.6 amps and was rated for 1.6 amps. Is this too close to rating ?? Should i be running slightly below rating on motor..?
    Houston,Tx.
    Quote Originally Posted by jmiles View Post
    Did it say on the motor that the RLA was "rated load amps" sometimes mfg. RLA stands for "running load amps" I know Ruud it seems like forever has always had RLA as "rated load amps".
    Chicago
    Thought fan motors have one rating unlike a compressor.. With FLA and RLA distinction..
    Jun 2013
    N. Canada
    RLA is "rated load amps".
    I even remember when this term was introduced in the 70's.
    That motor may be telling you that the rads not as clean as it looks!
    Check the charts re: SP vs HP.
    VA
    Quote Originally Posted by IRBH View Post
    I agree, if your meaning of rad is condenser coil. Higher run current on axial blades indicates an airflow restriction.
    Typically I see FLA label about a 10th above of operational reading.
    "The only true wisdom is in knowing you know nothing" Socrates
    Visit us at Dr. Degree°s HVAC
    or like us on Facebook
    Virginia
    with fans , you want it to pull the amps written on the tag
    if it says 1.6 , then pulling 1.6 is perfect
    over amping , and under amping fan motors is Bad , they will get hot .
    compressors on the other hand , like to run a couple of amps Under whats written on tag
    weird huh ....
    Jan 2006
    McQueeney, Texas
    I agree- 1.6 is fine.
    Jun 2013
    N. Canada
    Quote Originally Posted by Snapperhead View Post
    with fans , ..... under amping fan motors is Bad , they will get hot .
    weird huh ....
    Yeh, weird is the word. Or in old English, a load of crap!
    Think about it. You're a design engineer working on a new condensing unit. It calls for 5300cfm so you spec a 22" 27º fan run with a .5hp motor. So in a new rad it would be drawing full RLA. With a SF of 1 any load increase is overloading the motor. A small coil restriction to
    .10 SP Raises motor demand to .53 which is a 6% overload.
    They are not SUPPOSED to draw RLA.
    Virginia
    IRBH .... 6 percent isnt going to be enough to raise concern.
    But like i said , you want it close to the tag rating
    Chicago
    I ran a little test .. I blocked off 75% of the condenser with carboard and the amperage only moved from 1.6 up to 1.7 .. Dirty condensers make a miniscule difference inmho..
    Tallahassee, FL
    Some good reading materials on the subjects.
    Jul 2011
    East coast USA
    I glad you said that. I have battled many to make this point when dealing with coil cleaning-vs-money savings. I find it takes a lot in Most cases to warrant cleaning. if a system is running as designed, cleaning the coil will not make it run better also don't spend so much time killing yourself with bent fins. I have seen coils damaged by hail, run fine. The condenser coils are not sized for an exact ton. There is enough room that it takes a lot to jam it up...YES i know there are exceptions..but i rather clean my coils when i see a need and not have someone spray chemicals on them every year to make them shiny and leave residue on them so they can eat away at the pipe.
    Virginia
    99 percent of the time i just use water on outdoor unit
    yea maybe the amps on the fan dont change much , but the head pressure surely will with a dirty cond