Results 14 to 19 of 19
    Jun 2013
    N. Canada
    Sorry, with this Galaxy phone I can't see post & type.
    PHM said 55 SL, which is 41SH.
    Won't let me edit my post.
    They'll have to extend that 15 min just for me.
    Southold, NY
    PHM
    Go to the Scotsman site and download I believe the C series manual.
    Single evap 2-400 model
    Duel evap 600 model
    Please pose comp model for ref type
    Southold, NY
    CM series.
    Is this the machine you have?
    Jun 2012
    Wisconsin
    If you call Scotsman tech line they will help you out if your stuck, the guys they have in house are great. Does this unit have a hot gas defrost on the evaporator? I have had those things let refrigerant leak by. Water temp is very critical to these units. Another thing I would check is the position of the sensing bulb for the power head, and if the sensing bulb is insulated. TXV should also be insulated. All of these items will influence the system
    Oct 2009
    Raleigh, NC
    Don't all ice machines have hot gas defrost? And, on a CM cuber, incoming water temp has no effect on the refrigeration cycle, other than warm incoming water extends the cycle time slightly, of course.
    Dec 2012
    Illinois
    Looks like it's a little low on refrigerant with maybe a slightly clogged condenser. He did not have any R408 on the truck and the job's not critical enough to 'scramble' for. <g>
    What say you all? What's up with this puppy?
    I think your on it PHM!!
    I would probably put a clamp probe across that harvest valve to make sure it isn't bleeding, considering the age of this unit. (Early 90's?)