Results 14 to 26 of 45
    Virginia
    Virginia
    Oct 2012
    Where we mow our own grass
    True GDM-7
    Has a Tecumseh AE530AT-726-A4 1/5hp
    Specifies Cap Tube as 10' of 0.042id
    Virginia
    well alrighty then , cool thanks
    where do these little gems like to leak ?
    im adding shraders in the morning , a drier with port because Poodle will yell if I dont , and then pressurizing
    Oct 2011
    Chicagoland Area
    Quote Originally Posted by Snapperhead View Post
    It's a True. They either leak in the evap u-tubes or accumulator.
    Jul 2000
    Guayaquil, EC
    I think that filter-drier is the original. The bad brazing job is typical of True.
    For a replacement drier I prefer the Sporlan C032-CAP-T.
    Jul 2011
    Lehigh Valley, PA
    If that calls for a 10' cap tube, where is the rest of it rolled up? That cap tube in the pic does not look factory but the dryer does.
    Here's what I would do -
    OPTION 1
    The compressor runs
    The condenser fan runs
    The evap fan runs
    So first hose the whole thing out, especially the cond coil, with a garden hose so you're not working on some yakked up pos.
    Let it dry
    Then remove the drier
    Make sure nitrogen pressure comes through the cap tube
    Silphos a access valve onto the compressor's stub
    Replace the drier with one with an access valve on it.
    Pressurize to 150 with nitrogen. Leave overnight.
    If the pressure falls by morning - find the leak(s)
    If you can't find the leaks - evac, add some dye, and charge to ambient plus 30
    Let it run for a few days and then look for dye traces
    OPTION 2
    Give it to the scrap man and get back to work
    PHM
    like 3 foot tall , glass door , 134 10 oz
    customer had me take a peek while fixing a deli case
    No access ports ofcourse and i didnt have any pierce valves
    Cond had a small blanket of fur , cleaned that off
    Feeling around , the line line off compressor is kinda hot going to cond, and the compressor shell kinda hot as well , but the tube bends on the cond are ambient at top and bottom.
    drier has been replaced before judging by the aweful braze job , and its slightly cooler than ambient to touch
    all fans working fine
    I guess its time for another drier and cut out few inches of cap tube ?
    PHM
    Virginia
    i didnt leave nitro in all night because i have missplaced my gauge i use for testing
    Both coils clean
    replaced drier with one i had on truck forever 032 ( no port ) added shrader to the stub on shell , cut 6 inches of cap just incase ...
    added 7 oz and low side was at 5 , so i gave a squirt more and jumped to 20 , then settled out and its hanging around 12 psi
    amping 3.8 (RLA 4.4 on label )
    pulled down to temp within 15 min , sweet
    its 88 outside and humid on the porch , discharge line is 160 deg , drier filter 115 deg , box 29 degrees inside when it shuts off , then comes on at 48 degrees
    the knob was on 1
    moved knob to 5
    shut off at 27 deg , on at 48
    moved knob to 4
    shuts off at 29.7 , on at 48
    Need a new stat ?
    Mar 2013
    swan valley idaho
    you can adjust a little if its a ranco. otherwise get a a12-1506 for 38 cut in, or a12-701 for 41 cut in
    Eugene, Oregon
    deleted
    "The bitterness of poor quality remains long after the sweetness of low price is forgotten". --Benjamin Franklin
    "Don't argue with an idiot, they will drag you down to their level and beat you with experience". --Mark Twain
    http://www.campbellmechanical.com
    Jul 2011
    Lehigh Valley, PA
    Why didn't you charge 10ozs.? 12 psi with 134 is too low. I think you will be starving the evap with a heat load in the box.
    Chicago, IL
    Do you have anything in the cooler? If there's no product inside the temp will swing all over the place