    Quote Originally Posted by mark beiser View Post
    Whatever are you talking about?

    What is wrong with knee walls exposed to the attic with only R-11 batts and wall studs exposed to the attic, unsealed floor truss ends allowing attic air to circulate between the floors, unsealed duct chases open to the attic, unsealed/uninsulated pull down attic stairs in the conditioned space, black composition roof shingles, 30+ non air tight light fixtures, indifferently air sealed R4 insulated ducts and air handling equipment located in the attic, and 2 or 3 powered attic ventilators?


    Oh, since you put it THAT way...nothing at all!
    Psychrometrics: the very foundation of HVAC. A comfort troubleshooter's best friend.

  2. #22
    Join Date
    May 2013
    Location
    Utah
    Posts
    57
    Post Likes
    This is the Ask Our Pro's forum, and only Pro members that have been vetted by the AOPC may post advise, commentary, or ask questions of the OP here.

    You can find the rules for posting and qualifications here.

    Further infractions may result in loss of posting privileges.
    Last edited by beenthere; 06-23-2013 at 01:58 PM. Reason: Non Pro * member

  3. #23
    Join Date
    Jan 2009
    Location
    SE Iowa
    Posts
    5,577
    Post Likes
    Sounds like the system is oversized anyway. A 7f drop on a 95f day in most climates should take over 8 or 10 hours to recover But it only needs low stage to maintain 75f in those conditions.

    As mentu setbacks don't save. You must deferred all your runtime to the hottest and least efficiency operating conditions. Small setbacks make sense with time of use metering, but that's about it.

    Sent from my DROID RAZR using Tapatalk 2

  4. #24
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    StarCat, this is the Ask Our Pro's forum, and only Pro members that have been vetted by the AOPC may post advise, commentary or ask questions of the OP here.

    You can find the rules for posting and qualifications here.

    Your post has been deleted.
    Further infractions may result in loss of posting privileges.

  5. #25
    Join Date
    Jul 2012
    Posts
    44
    Post Likes
    Thread Starter
    Quote Originally Posted by jacob-k View Post
    generally better equipment, more efficient equipment will have more surface area to remove heat, but not always is the new stuff as big as the old stuff.....As stated i would start with a Superheat/subcool reading (system charge), I personally would like to see a temperature split on the coil, or what we call a delta t. the target at the coil should be somewhere around 20. it can be done at the registers and return but it would be far less accurate. but chances are if the tech finds it low he will charge it to spec (hopefully) and call it good.
    The tech just left. He determined the issue to be either an overcharge or a faulty TXV meter, as he read a wavering temperature split when he plugged in his device. He tried releasing some freon to bring the charge down, but it didn't fix the readings so he's called for a new TXV meter install tomorrow. Hopefully that fixes the problem, will update tomorrow after complete.

  6. #26
    Join Date
    Feb 2013
    Location
    Sonora, California, United States
    Posts
    8,383
    Post Likes
    Quote Originally Posted by Johnnyma45 View Post
    The tech just left. He determined the issue to be either an overcharge or a faulty TXV meter, as he read a wavering temperature split when he plugged in his device. He tried releasing some freon to bring the charge down, but it didn't fix the readings so he's called for a new TXV meter install tomorrow. Hopefully that fixes the problem, will update tomorrow after complete.
    he just released some freon? he didnt put it in anything?

  7. #27
    Join Date
    Jul 2012
    Posts
    44
    Post Likes
    Thread Starter
    Quote Originally Posted by jacob-k View Post
    he just released some freon? he didnt put it in anything?
    Not that I saw, no.

Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •