    liquid line comes into box, goes through a 163 filter then through a pump down solenoid...then it tees off one line hugs the suction line then into the tev...the second liquid line bypasses the tev and it goes into the line coming out of the tev between the distribution tube and tev...
    whats that?
    Let's give nukes a chance.
    California
    That line bypassing the TEV should have a check valve in it. Because it's the return line for gas defrost.
    Dec 2009
    B.C.
    The part located between the TXV and the distributer is an Auxiliary Side Connecter (ASC). This may be a system that uses either a method of capacity control, like 'Bypass to Evaporator', or uses a method of defrost, like hot gas defrost.
    May 2005
    i can see the electric heater in the drain area...how does it work cause theres only one solenoid..anyone have a cartoon of this system?
    also when this systems goes into defrost, it pumps down and compressor shuts off.
    Jul 2011
    Ontario, Canada
    Quote Originally Posted by primmers View Post
    If system is pumping down on defrost then don't think it is hot gas defrost. Case must have had heaters added to change to electric defrost.
    Sent from my iPad using Tapatalk HD
    Mar 2013
    NJ
    Klixons clamped to return bends will operate relays in kick plate to turn on door anti sweats when case is in refrigeration, and turn fans off, supplemental heater on when defrost is started , if its hot gas. Might be a gas defrost case converted to electric. Look for contactor controlled by #3 terminal of clock, or if its just a single case #3 might go right to heaters. Wiring will probably be field modified, defrost power in case pan will also power a relay in kick plate to turn off fans for defrost, won't turn back on till fan delay klixon on return bend makes.
    It is probably a case that was originally piped for gas defrost that was subsequently used on an electric defrost system.
    Think defrost on a heat pump and you'll get the general concept.
    May 2005
    thanks guys..
    Virginia
    does this have 2 thermostats ?
    Maybe theres one hidden under another sheet metal cover along with another solenoid for the hot gas defrost ?
    Maybe someone has removed some things and frankensteined it ..... we love to do that ya know
    Jan 2010
    Sea to Sky
    The heater around the drain is your drain pan heater. This is a low wattage heater to keep ice out of the drain. If it has been converted to electric defrost, you are going to have at a minimum one additional heater, possibly more, to defrost the coil.
    May 2005
    this case has been modified..but its running now...