    I have 2 CVHE side by side in parallel, they have isolation valves on chilled water,that open when chiller is on. On the one chiller the isolation valve don't hold and when the chiller is off, chilled water gets circulated through the barrel. This machine keeps getting air in it, Another mechanic leak checked the machine and said the reason it is getting air in it, is due to chilled water being circulated through the bundle in off cycle and pulling air in through purge. First is this possible and if so how?
    ottawa canada
    What kind of purge is on the chiller , Purifier or Earthwise . Has anyone ever changed the solenoids on the purge . If its a purifier the big mistake is to install the solenoids with the flow arrows pointing in the direction of flow on both solenoids . This is incorrect they should oppose each other .
    Try valving the purge off and see if it sucks air , if it doesnt then pressurize the purge with nitrogen and fix the leaks . They should not suck air in they should hold both pressure and vacuum .
    Aug 2000
    Phila, PA
    Quote Originally Posted by Healey Nut View Post
    It's a purifier( I believe), I haven't seen this job yet but will be there tomorrow. And I will check the above. So what your telling me is that sucking air in via purge because chilled water isolation valve is bad and letting chilled water pass in off cycle is not normal correct? Our senior chiller mechanic is who told me this, I've been working under him learning chiller's for the last 3 years. When he told me this it made no sense to me and when I questioned it, he sounded like a politician and I could not get a straight answer.
    ottawa canada
    Quote Originally Posted by fr420 View Post
    Chiller off chiller on, flow no flow makes no difference if its suckin air its got a leak period .
    Sounds to me like you have a high side leak on that machine , it sucks air in because the whole chiller is in a vacuum no just the evap when its idle .
    Go over the chiller with a set of wrenches and check ALL the flat gasket joints for torque .
    Aug 2000
    Phila, PA
    Ok thanks, That's what I thought but this guy has more experience then me on low pressure machines and just wanted to make sure I wasn't missing something.
    age does not equal intelligence.
    lots of years in the trade does not equal 'smarts' either.
    Aug 2009
    Prattville, Alabama
    Reminds me of something I heard long ago: "There's a difference between 10 years of experience, and 1 year of experience repeated 10 times".
    Aug 2009
    Jurupa Valley, CA
    No, chillers should not leak - that said, no system is perfect, so the fact that the chilled water continues to flow through the evaporator keeps them at a vacuum, exasperating any potential leaks that may be there. We have 5 CVHE's of various age, and they all have "pre-vac" heaters on them to keep the system neutral when offline - of course, if the chilled water is flowing, the heaters aren't going to keep up with them, and it will be sitting at a vacuum. Is the chilled water flow the cause of your leak? no, but if it wasn't flowing, you would not be leaking near as much (I think the zero point of R-11 is about 75°F or so, so if it wasn't flowing, and the water came up to room ambient, the leakage would effectively stop).
    Oct 2010
    Link gone
    Oct 2010
    isolate the purge from the chiller,and leak check the purge with nitro, not only the solenoids will leak, also the float switch that is located on the bottom of the cannister,and go up in pressure when you are leak checking the purge with nitro,
    Jul 2013
    N.H.
    Leaking though the purge should be eliminated if the purge was installed with an isolation valve. The chiller probably is leaking. Check your purge rates. If you have excessive purge rates you should leak check the whole chiller. The discharge veloute is a usual suspect.Use hot water to bring the pressure up to 8 lbs but never higher than 10 or you may rupture the relief. The relief if set to fail at 15 psig.