    Totally understand that mgibbs. It may be something you just put in your notes to help with diagnostics should other problems arise with this system.
    the piston or orifice is not seating up tight and bypassing some freon
    Aug 2001
    Mechanicsville, Virginia
    OD dry bulb?, indoor wet bulb? SEER? Need these three more to obtain diagnosis.
    South Texas
    take some temp readings on your return bends of the evap, you may have a restriction and some one has overcharged it and is overfeeding on the unrestricted areas of the coil
    Jun 2013
    N. Canada
    Unless I missed it, how can the discussion have gotten to this point (and conclusions reached) without any mention of Ambient temp, at the very least?
    May 2013
    near knoxville tenessee
    Quote Originally Posted by IRBH View Post